I've been able to trap a few MIB's, but where the heck is the full list?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 12:53 AM . Last Modified: 2024-03-19 02:44 AM
Hi,
On 2/7/2019 1:00 PM, George said:Do you know of a free powerSNMP tool?
Yes. Just enter powersnmp free manager into your favorite search engine. The one I like is from Dart.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 12:52 AM . Last Modified: 2024-03-19 02:44 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 12:52 AM . Last Modified: 2024-03-19 02:44 AM
Here's one I trapped and turned into an email alert.
trapargsString:= UPS: A fault exists at the battery temperature sensor.
snmpTrapOID:= PowerNet-MIB:apc.0.600 (1.3.6.1.4.1.318.0.600)
Here's another:
mtrapargsString:= UPS: The battery is not installed properly.
snmpTrapOID:= PowerNet-MIB:apc.0.80 (1.3.6.1.4.1.318.0.80)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 12:52 AM . Last Modified: 2024-03-19 02:44 AM
Hi,
What I do is use a tool like powerSNMP and navigate to the UPS or product and review the available OIDs. All APC products have an OID that starts with OID=.1.3.6.1.4.1.318 You can also walk the device to see the OIDs.
As an example if I what to know the UPS model OID I check the app and found 1.3.6.1.4.1.318.1.1.1.1.1.1
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 12:52 AM . Last Modified: 2024-03-19 02:44 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 12:52 AM . Last Modified: 2024-03-19 02:44 AM
Why aren't the available OIDs in document form already to hand to the end users?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 12:52 AM . Last Modified: 2024-03-19 02:44 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 12:52 AM . Last Modified: 2024-03-19 02:44 AM
Do you know of a free powerSNMP tool?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 12:53 AM . Last Modified: 2024-03-19 02:44 AM
Hi,
On 2/7/2019 1:00 PM, George said:Do you know of a free powerSNMP tool?
Yes. Just enter powersnmp free manager into your favorite search engine. The one I like is from Dart.
Link copied. Please paste this link to share this article on your social media post.