What to do when you have more UPS's than you need?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • What to do when you have more UPS's than you need?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:15 AM . Last Modified: ‎2024-03-08 02:43 AM

0 Likes
3
947
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:15 AM . Last Modified: ‎2024-03-08 02:43 AM

What to do when you have more UPS's than you need?

Current configuration: 9 Servers connected to 9 UPSs (2200 or 1500s)

Future configuration after some Server consolidation:6 Servers connected to 9 UPS (same 2200 or 1500s)

All my servers have dual power supplies.

Is there a "best practices" of what do do when you have extra UPSs? Do people ever connect them serially? (Outloot > UPS > UPS > Server) Put one UPS per power supply on the most import servers?

Just curious.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-30 05:15 AM . Last Modified: ‎2024-03-08 02:43 AM

0 Likes
0
947
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:15 AM . Last Modified: ‎2024-03-08 02:43 AM

As long as the number of UPS' you have meet your runtime and redundancy needs...there's not really a "best practice" approach to this situation although it sounds like you've found an acceptable configuration. If you are referring to "daisy chaining" when you asked about UPS > UPS, we cannot support that since it does not meet UL specifications and can actually interfere with normal UPS performance. Sharing multiple power supplies among UPS' is not an issue as long as each power supply has a redundant source. Having one UPS per power supply will ensure that the supply has the maximum amount of runtime it can be provided and will probably ensure you better runtime and prevent any risk of overload.

However, if you find that everything is working for you currently and there are no runtime shortages and none of the UPS' are close to overload...you could always distribute those UPS' to another location within your facility.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-30 05:15 AM . Last Modified: ‎2024-03-08 02:43 AM

0 Likes
0
947
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:15 AM . Last Modified: ‎2024-03-08 02:43 AM

Marked as answered due to date of last response.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-30 05:15 AM . Last Modified: ‎2024-03-08 02:43 AM

0 Likes
0
948
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:15 AM . Last Modified: ‎2024-03-08 02:43 AM

As long as the number of UPS' you have meet your runtime and redundancy needs...there's not really a "best practice" approach to this situation although it sounds like you've found an acceptable configuration. If you are referring to "daisy chaining" when you asked about UPS > UPS, we cannot support that since it does not meet UL specifications and can actually interfere with normal UPS performance. Sharing multiple power supplies among UPS' is not an issue as long as each power supply has a redundant source. Having one UPS per power supply will ensure that the supply has the maximum amount of runtime it can be provided and will probably ensure you better runtime and prevent any risk of overload.

However, if you find that everything is working for you currently and there are no runtime shortages and none of the UPS' are close to overload...you could always distribute those UPS' to another location within your facility.

Reply

Link copied. Please paste this link to share this article on your social media post.

EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: ‎2021-06-30 05:16 AM . Last Modified: ‎2024-03-08 02:43 AM

0 Likes
0
947
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:16 AM . Last Modified: ‎2024-03-08 02:43 AM

Yes, plugging each power supply into seperate UPS's is a common practice. To be truely redundant, obviously both your power sources should be different, even a different circuit isn't a bad idea.

For redundant setups, I'd even recommend putting network management cards in each UPS. (part number ap9617, ap9618, ap9619)

You can install a Power Network Shutdown agent on each server attached to the 2 UPS's and configure the single agents to talk to multiple cards. This is great in that when a critical event like "low battery" happens to one unit and not the other, the software doesn't bother shutting down your systems. It will effect it when you have critical events on both UPS's.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore