When i do prioritization on VM's in the High, Medium, Low Section, where do i put the vCenter VM. because that one has to go out as latest one.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:17 AM . Last Modified: 2024-03-08 02:42 AM
Hi,
You do not need to prioritize vCenter VM. All other VMs will be powered off, then the vCenter VM, the hosts and finally the host running PCNS VM and the PCNS VM will go down last.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:17 AM . Last Modified: 2024-03-08 02:42 AM
Hi,
You do not need to prioritize vCenter VM. All other VMs will be powered off, then the vCenter VM, the hosts and finally the host running PCNS VM and the PCNS VM will go down last.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.