What setting do I need to allow PCNS appliance to automatically restart after failure?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • What setting do I need to allow PCNS appliance to automatically restart after failure?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
122
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:21 AM

0 Likes
5
1150
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:21 AM

What setting do I need to allow PCNS appliance to automatically restart after failure?

I am running ESXi 7.0 on a two host cluster but currently don't have HA or DRS enabled as I am beginning to configure everything. I do however want to make sure PCNS is configured correctly in case of a power outage.

I read in the vmware guide (correct me if i am wrong) that in order to successfully allow the PCNS appliance to auto start is to enable HA. Is this the correct setting?

oieD7hsk1IJjTlBKP9RI6g%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngoieD7hsk1IJjTlBKP9RI6g%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

 

I simply want to make sure that when everything starts back up after a power failure, that the Powerchute appliance auto starts in order to restore all hosts and VMs.

Thank you.

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:21 AM

0 Likes
0
1148
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:21 AM

Lee,

When running the PowerChute virtual appliance configured with vCenter for the PowerChute appliance to restart automatically with the host you must

1 - configure HA and select Host failure response = Restart VMs.

or 

2 - enable Autostart on the host for the PowerChute VM. See Schneider Electric FAQ FA159688

If you do not do one of those two, when the host is started the PowerChute VM will need to be started manually. 

As Gavan wrote earlier, for the hosts to restart automatically when AC is restored you must configure the BIOS of the server to power on when AC is restored. 

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:21 AM

0 Likes
0
1148
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:21 AM

Hi Lee,

The Powerchute appliance can't turn your machines back on.

You need to modify the server's BIOS to ensure that recovery after AC failure is turned on, this will boot the physical server after a power failure, you would need to contact your server manufacturer to find out how to do this on their specific hardware.

Next, you need to configure your VMWare to boot the VMs, this would be a question for VMWare but the link below should help:

https://docs.vmware.com/en/VMware-vSphere/6.7/com.vmware.vsphere.vm_admin.doc/GUID-5FE08AC7-4486-438...

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:21 AM

0 Likes
0
1148
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:21 AM

On 1/28/2021 6:18 AM, Gavan said:

Hi Lee,

The Powerchute appliance can't turn your machines back on.

You need to modify the server's BIOS to ensure that recovery after AC failure is turned on, this will boot the physical server after a power failure, you would need to contact your server manufacturer to find out how to do this on their specific hardware.

Next, you need to configure your VMWare to boot the VMs, this would be a question for VMWare but the link below should help:

https://docs.vmware.com/en/VMware-vSphere/6.7/com.vmware.vsphere.vm_admin.doc/GUID-5FE08AC7-4486-438...

-Gavan

Hi Gavan, 

I think you misunderstood my question. I actually meant what setting is needed for the Powerchute appliance to auto start when the hosts are restored from a power outage. For example, power goes out, powerchute gracefully shuts down all vms and hosts. Power is restored and all hosts are back online but now powerchute must restart itself in order bring other hosts out of maintenance mode and start the vms back up.

I believe something needs to configured in order for powerchute auto start and I remember reading somewhere that it may be a HA setting. 

I hope this clears it up. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:21 AM

0 Likes
0
1148
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:21 AM

As I said above, you just need to configure to configure VMWare to turn the PCNS VM and all other VMs back on after the power is restored.

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:21 AM

0 Likes
0
1148
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:21 AM

Thanks Gavan.

I was under the impression that some sort of HA configuration was needed to allow PCNS to autostart. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:21 AM

0 Likes
0
1149
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:21 AM

Lee,

When running the PowerChute virtual appliance configured with vCenter for the PowerChute appliance to restart automatically with the host you must

1 - configure HA and select Host failure response = Restart VMs.

or 

2 - enable Autostart on the host for the PowerChute VM. See Schneider Electric FAQ FA159688

If you do not do one of those two, when the host is started the PowerChute VM will need to be started manually. 

As Gavan wrote earlier, for the hosts to restart automatically when AC is restored you must configure the BIOS of the server to power on when AC is restored. 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of