What is the high voltage threshold that causes a SMART UPS 5000 XL to advise that bypass is out of range : High Voltage?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • What is the high voltage threshold that causes a SMART UPS 5000 XL to advise that bypass is out of range : High Voltage?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:25 AM

0 Likes
8
4265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:25 AM

What is the high voltage threshold that causes a SMART UPS 5000 XL to advise that bypass is out of range : High Voltage?

I'm getting a lot of these messages from a new 5000 XL that replaced an older unit.  I didn't see any alerts on the older unit.

The new UPS is using the same power source.  Nominal output voltage is set to the default of 230 volts and in the logs I can see VMAX  hits 250v occasionally. 

The upper bypass limit is default at 255v so I am surprised that the unit alerts me to inputs of 250v, unless of course the logs are not picking up the actual highest recorded voltage?

Any info / advise, much appreciated.  The fix may be as simple as setting the nominal output voltage to 240 so that the difference is not as great.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:24 AM

0 Likes
0
4262
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:24 AM

If the voltage was too high, the UPS would go to battery power so I wouldn't worry about that.

And also, I would venture to guess maybe the log isn't catching short voltage peaks over 255 but then I would think you wouldn't see it in the log either. Considering it is hitting/logging 250V, I would think it is getting really close to 255 at some point.

In the EMEA region, 230V is the nominal voltage so if it is consistently at 250V+ I would investigate why that is as you suggested Allan. I don't see any load fluctuations on the UPS, like a drop in current to increase voltage or something, but there may be something happening on the UPS circuit itself to cause a periodic spike in the voltage or something further upstream.

Either way, the UPS is indeed just giving you a warning saying it is seeing high voltage, if it has to go to bypass (overload, fault, etc), it won't go and expose the load to the high voltage and will likely turn off. It will require investigation into the input power/circuit.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:25 AM

0 Likes
0
4262
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:25 AM

Hello,

Can we take a look at your logs? You can remove any sensitive information if you want. It'd be helpful to take a look.

Instructions on obtaining logs (event, data, config) from the Network Management Card are here -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...

Also, what is the nominal voltage in your region? It sounds like 230V and the exact SKU of your UPS (from the white barcode sticker on it) is SURTD5000XLI - could you confirm? Do you know the previous UPS model you had?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:25 AM

0 Likes
0
4262
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:25 AM

Hi Angela, can I attach / upload the zipped up logs to this forum, or do they need to cut & pasted?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:25 AM

0 Likes
0
4262
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:25 AM

Yep. You can put them here. When you're typing your reply, select "Use advanced editor" on the top right of the apply box and it will show an option to attach files.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:25 AM

0 Likes
0
4262
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:25 AM

Hi Angela, sorry but I cannot see any option to use advanced editor or attach files, aside from an image or video. I cannot see an "apply" box. Sorry if I am missing something obvious.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:25 AM

0 Likes
0
4262
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:25 AM

Make sure you're viewing the thread outside of your Inbox - If you reply right from your communications inbox, you only see comment/cancel and no editor versions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:25 AM

0 Likes
0
4262
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:25 AM

Hi,

I also have the same issue with the same UPS. Keep getting notified of the following.

Critical Events - UPS: Bypass not in range ; high voltage.

Information Events - UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.

The data logs show the input voltage passing 250 VAC, which triggers the notification, although the bypass upper voltage is 255 VAC

The power settings/ thresholds on the UPS are

UPS - POWER

Rated Output Voltage - 230 VAC

Bypass Upper Voltage - 255 VAC

Bypass Lower Voltage - 160 VAC

 

Output Frequency Range - Auto Hz

I have attached the DATA and EVENT log files.

Can I stop the email notifications?

Does the high voltage cause a problem for the UPS?

Thanks, Dan.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:24 AM

0 Likes
0
4262
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:24 AM

Interesting that this hasn't been asnswered.  I am wondering if this is an issue with the newer UPS as I didn't see it on the older model.

You can stop the notifications Dan. If genuine this high voltage could cause problems for equipment if you were, say manually in bypass for any reason. The system is warning you though that if for any reason it needed to go into bypass, at that time, it couldn't because the voltage is out of range.

Would be great if someone with more knowledge on the matter is able to advise further.

May also be worth speaking with you building Facility managment team to enquire about getting the supply checked.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:24 AM

0 Likes
0
4263
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:24 AM

If the voltage was too high, the UPS would go to battery power so I wouldn't worry about that.

And also, I would venture to guess maybe the log isn't catching short voltage peaks over 255 but then I would think you wouldn't see it in the log either. Considering it is hitting/logging 250V, I would think it is getting really close to 255 at some point.

In the EMEA region, 230V is the nominal voltage so if it is consistently at 250V+ I would investigate why that is as you suggested Allan. I don't see any load fluctuations on the UPS, like a drop in current to increase voltage or something, but there may be something happening on the UPS circuit itself to cause a periodic spike in the voltage or something further upstream.

Either way, the UPS is indeed just giving you a warning saying it is seeing high voltage, if it has to go to bypass (overload, fault, etc), it won't go and expose the load to the high voltage and will likely turn off. It will require investigation into the input power/circuit.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of