Smart-UPS SURTA1500XL powering Parasound JC1 monoblock amplifiers, overload on startup harmful?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS SURTA1500XL powering Parasound JC1 monoblock amplifiers, overload on startup harmful?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:24 AM

0 Likes
3
1100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:24 AM

Smart-UPS SURTA1500XL powering Parasound JC1 monoblock amplifiers, overload on startup harmful?

I have my SURTA1500XL hooked up to two Parasound JC1 monoblock amplifiers for my stereo, rated at 400W each. I don't play them very loud, at steady-state they show up as each using 30% load (2 lights on the load meter).

However, when I first turn on the amps, they spike the overload light briefly. Even turning on one amp will do this, the second amp briefly lights up the overload light and the APC also briefly chirps at me.

1) Does this activate the surge protection circuitry, and will repeated use quickly wear out my APC or its ability to protect my equipment? I turn on and off the stereo several times per day.

2) Will this in any way harm my amplifiers, or blow any of their fuses etc? Is not being able to draw the initial current spike somehow detrimental?

3) Would the initial current spike of the amps affect any other components plugged into the APC?

3) Will regularly running the APC at 80% load drastically reduce its life?

(note that with turning on the rest of my stereo equipment, the load meter goes up to 80% (5 / 6 lights))

I would like to keep my amps plugged in to the APC because of the online topology and clean power I can provide to the whole system, which significantly helps to improve the quality and depth of the sound output, I'm not that concerned that the batteries would only last a short while during a power event, but I'm just a little concerned about drawing that much current from the APC and the overload light.

Thanks for your help.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:24 AM

0 Likes
0
1100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:24 AM

1) A brief current overload may depress the line voltage depending on the magnitude of the surge and the conditions of your electric wiring, however this isn't a big concern. If the line voltage did go down, the UPS would go to battery briefly. I don't think such a voltage depression would significantly affect surge suppression... it's just not very much energy. Surge protection does wear out over time as it suppresses the surges from the power lines.

2) It will not harm your amplifiers. The overload indication is mainly to warn you that the UPS may not be able to sustain the load on battery, although SmartUPSes are designed to handle a brief overload. The easy way to test this is to pull the plug and see if the amps work while the UPS is on battery. You can also try turning them on while on battery to see if the UPS can handle the initial surge. The initial surge may not matter to you if you aren't turning the amps on during a power outage.

3) The initial spike of current shouldn't affect other components plugged into the UPS unless the wiring is soft enough that it depresses the voltage (which you can tell if the UPS goes on battery). And if it does depress the voltage, most devices should not care. No device should be damaged. For example, a laser printer on the same circuit will often depress the voltage enough when it starts to trigger a UPS to go to battery, but computers on the circuit are completely unaffected.

4) Running a UPS at high loads is APC's recommended way to operate them because it's more efficient than a UPS under low load. It should not reduce lifespan significantly, although like battman says, depth and frequency of battery discharge affects how long the battery lasts.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:24 AM

0 Likes
0
1100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:24 AM

I have my SURTA1500XL hooked up to two Parasound JC1 monoblock amplifiers for my stereo, rated at 400W each. I don't play them very loud, at steady-state they show up as each using 30% load (2 lights on the load meter).

However, when I first turn on the amps, they spike the overload light briefly. Even turning on one amp will do this, the second amp briefly lights up the overload light and the APC also briefly chirps at me.

1) Does this activate the surge protection circuitry, and will repeated use quickly wear out my APC or its ability to protect my equipment? I turn on and off the stereo several times per day.

2) Will this in any way harm my amplifiers, or blow any of their fuses etc? Is not being able to draw the initial current spike somehow detrimental?

3) Would the initial current spike of the amps affect any other components plugged into the APC?

3) Will regularly running the APC at 80% load drastically reduce its life?

(note that with turning on the rest of my stereo equipment, the load meter goes up to 80% (5 / 6 lights))

I would like to keep my amps plugged in to the APC because of the online topology and clean power I can provide to the whole system, which significantly helps to improve the quality and depth of the sound output, I'm not that concerned that the batteries would only last a short while during a power event, but I'm just a little concerned about drawing that much current from the APC and the overload light.

Thanks for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:24 AM

0 Likes
0
1100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:24 AM

HI there,

You may already be aware of this but thought it worth mentioning that your Parasound Amps have a "soft-start" circuit utilizing NTC's (negative temperature coefficient resistors) to reduce the inrush current drawn by its toroidal power transformer and while charge the capacitors (4 x 33,000 uF), then a relay kicks in to bypass the NTC's for full input current. My comments / answers re your questions are:

Most of the smart-ups input/surge protection circuitry is designed to reduce harmful voltage spikes, not current spikes. There are inline inductors designed to filter out EMI/RFI noise on the incoming power but these are high current devices...Eg upwards of 22 Amps. Your Parasound Amps may actually generate a voltage spike when they are turned off as the magnetic field in the transformer collapses, but perhaps Parasound's engineers have included circuitry to prevent that from going back out on the line (Can't tell from the online searches I did)...any such spikes would hit the output circuitry on the UPS, not the input. Current flow within the ups does pass thru some relays (Eg Bypass / PFC ) which will have to handle a brief current surge, however with relays its more the make/break action that wears them out. When your ups chirps at you does it make any mechanical switching or clicking noises ? Once these UPS are overloaded, if its a sustained overload they will usually not kick to battery but could shut off as  a protective measure to prevent damage to the IGBT transistors in the UPS inverter/charger stages.

You say your load bar graph is showing 2 bars - this could actually represent up to a 49 % load, not 30%. If 4 bars are lit up that's 80% , 5 bars is 100 %.

The higher the load on your ups, the slightly shorter the lifespan of the batteries will be as the depth of discharge of the batteries during the 14 day self test (or actual power outage) is directly proportional to load....higher depth of discharge means shorter battery lifespan.

The SURTA1500 is capable of 1050 watts of real power output (not 1500), so to me it would seem like having these two high power Amps plus all your other gear is a bit too much. Your Amps can put out up to 800 watts into 4 ohms and 1200 watts into 2 ohms .... 400 watts is only at 8 ohms and no speaker maintains that impedance value over all input frequencies...between 20Hz and 20kHz it can drop lower than 8 or be higher. Repeatedly having the ups report overload represents an electrical strain on it that it wasn't meant to handle, so I believe over time some degradation of the UPS is definitely possible, but not the Amps.

If this were my setup I might put the Amps on a power conditioning device (surge arrest/noise suppression) but not a full blown UPS. Nothing wrong with having your source devices and preamps on a UPS though !

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:24 AM

0 Likes
0
1101
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:24 AM

1) A brief current overload may depress the line voltage depending on the magnitude of the surge and the conditions of your electric wiring, however this isn't a big concern. If the line voltage did go down, the UPS would go to battery briefly. I don't think such a voltage depression would significantly affect surge suppression... it's just not very much energy. Surge protection does wear out over time as it suppresses the surges from the power lines.

2) It will not harm your amplifiers. The overload indication is mainly to warn you that the UPS may not be able to sustain the load on battery, although SmartUPSes are designed to handle a brief overload. The easy way to test this is to pull the plug and see if the amps work while the UPS is on battery. You can also try turning them on while on battery to see if the UPS can handle the initial surge. The initial surge may not matter to you if you aren't turning the amps on during a power outage.

3) The initial spike of current shouldn't affect other components plugged into the UPS unless the wiring is soft enough that it depresses the voltage (which you can tell if the UPS goes on battery). And if it does depress the voltage, most devices should not care. No device should be damaged. For example, a laser printer on the same circuit will often depress the voltage enough when it starts to trigger a UPS to go to battery, but computers on the circuit are completely unaffected.

4) Running a UPS at high loads is APC's recommended way to operate them because it's more efficient than a UPS under low load. It should not reduce lifespan significantly, although like battman says, depth and frequency of battery discharge affects how long the battery lasts.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore