SURTD5000XLi does not hold load

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SURTD5000XLi does not hold load
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:24 AM

0 Likes
9
1765
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:44 AM . Last Modified: ‎2024-03-12 03:24 AM

SURTD5000XLi does not hold load


Good afternoon

Have a SURTD5000XLi that has been lost for a while (a few years actually)

Installed new RBC44 battery kit, unit cold starts.

Powering on gives warning of failed batteries that goes away a few minutes later

Letting batteries charge (which they do (~ 219Vdc ) with mains until full

Terminal gives a few hours on runtime remaining but has soon as I pull the plug, the load is cut off

Trying to perform calibration immediatly cuts load also, and is a PITA to try to start the UPS after a failed calibration aptempt ....

Any suggestion anyone?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:45 AM . Last Modified: ‎2024-03-12 03:24 AM

0 Likes
0
1765
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:45 AM . Last Modified: ‎2024-03-12 03:24 AM

I forgot to ask and I re-read and didnt see it noted. Does the UPS coldstart? Meaning if you remove AC power from it and unplug it and hold down the test button, the UPS should beep twice and then you should hold and let go of the test button during the second beep?

This would normally sound like a battery issue but you said these batteries were brand new, right?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:45 AM . Last Modified: ‎2024-03-12 03:24 AM

0 Likes
0
1765
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:45 AM . Last Modified: ‎2024-03-12 03:24 AM

Thank you for sharing your findings. I am glad you were able to save it and get it working!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:45 AM . Last Modified: ‎2024-03-12 03:24 AM

0 Likes
0
1765
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:45 AM . Last Modified: ‎2024-03-12 03:24 AM


Good afternoon

Have a SURTD5000XLi that has been lost for a while (a few years actually)

Installed new RBC44 battery kit, unit cold starts.

Powering on gives warning of failed batteries that goes away a few minutes later

Letting batteries charge (which they do (~ 219Vdc ) with mains until full

Terminal gives a few hours on runtime remaining but has soon as I pull the plug, the load is cut off

Trying to perform calibration immediatly cuts load also, and is a PITA to try to start the UPS after a failed calibration aptempt ....

Any suggestion anyone?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:45 AM . Last Modified: ‎2024-03-12 03:24 AM

0 Likes
0
1765
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:45 AM . Last Modified: ‎2024-03-12 03:24 AM

Hello - when you refer to "terminal," are you talking about connecting via the serial port to the pre-installed UPS Network Management Card or are you talking about something else?

Can you describe the warning of failed batteries - is this the replace battery LED or another LED that is solid or flashing?

Here is the front panel for reference:

2196_smartupsRTFront.jpg

I'd be very interested in the UPS Network Management Card logs, if available. (Instructions here -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...)

Is it possible to retrieve those or at least verify if you have a Network Management Card (likely AP9619 or AP9631) installed? I believe this UPS ships with one.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:45 AM . Last Modified: ‎2024-03-12 03:24 AM

0 Likes
0
1765
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:45 AM . Last Modified: ‎2024-03-12 03:24 AM

Hello Angela

The led that flashed whem cold booting the UPS was the replace batteries one (led immediatly above power on button)

This ups comes pre-installed with AP9619, but i've accessed terminal via the 940-1525A RJ48 cable provided  (was actually trying to check if battery constant was OK ). I am going to power down the unit, plug in the AP9619 and send you the logs requested

FYI the unit's serial is : NS1002005141

Thank you for you support

Attachments
apcftp.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:45 AM . Last Modified: ‎2024-03-12 03:24 AM

0 Likes
0
1766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:45 AM . Last Modified: ‎2024-03-12 03:24 AM

Thank you for the logs. Just one note - SURTD units (versus SURT or SURTA) don't allow any type of access, like to change battery constants. SURTD units only offer the "RT Control Menu" and are micro-link language which a user cannot interact with. Plus, I don't think this issue has anything to do with battery contacts/runtime, etc...yet.

I looked at the logs and all honestly I don't really see anything abnormal!

When the load turns off upon unplugging the UPS, what does the UPS do? Does it report it is on battery with 4 beeps every 30 seconds and on battey LED (I didn't see any "on battery events in the log")? Alternatively, does the UPS turn off completely too? Or can you leave the NMC in and pull the plug and see what it logs?

Just to see, when the UPS goes to battery, assuming it stays on but just drops the output, can you measure with a voltmeter any of the receptacles on the output? Is there any AC voltage there, even if it is too low)? What is connected to the UPS for your testing, and whatever it is, is it plugged directly into the receptacle in the rear of the UPS, versus via a transformer? According to the data log, it thinks it is outputting 230V...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:45 AM . Last Modified: ‎2024-03-12 03:24 AM

0 Likes
0
1766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:45 AM . Last Modified: ‎2024-03-12 03:24 AM

Hello once again Angela

When unpluging the mains from UPS, it completly shuts itself down (fan stops also)

Powering it up, it reports Battery LED and the 4 beeps every 30 seconds ... After some time it stops beeping, battery led turns off and battery charge graph resumes until 100% . When I power on the unit, it is charging the batteries with 219Vdc

The load is a pure resistive one. It is a halogen projector, and when I pull the plug, it drops to 0V , because it shuts down the entire UPS (the relays switch....)

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:45 AM . Last Modified: ‎2024-03-12 03:24 AM

0 Likes
0
1766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:45 AM . Last Modified: ‎2024-03-12 03:24 AM

I forgot to ask and I re-read and didnt see it noted. Does the UPS coldstart? Meaning if you remove AC power from it and unplug it and hold down the test button, the UPS should beep twice and then you should hold and let go of the test button during the second beep?

This would normally sound like a battery issue but you said these batteries were brand new, right?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:45 AM . Last Modified: ‎2024-03-12 03:24 AM

0 Likes
0
1766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:45 AM . Last Modified: ‎2024-03-12 03:24 AM

Hi smile

Sometimes trying to coldstart the UPS fails ( first touch on power fan spins (brains on) but when trying to turn it on we can see and ear it trying to power , but the fan immediatly stops ) . It repeats this process 3 or 4 times

Powering it with mains, the fan starts and then we can turn it on. After some time charging the batteries, and if there is no load, unit coldstarts perfectly

Electronically, I've done all the tests I could. Browsing the internet I could find the service manual, and I can say that this lynx 2 board passes in all diode checks...

Thanks for all your effort smile

Forgot to say ,so I edited this reply: RBC44 kit is new (batteries quality test is of January 2013)

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:45 AM . Last Modified: ‎2024-03-12 03:24 AM

0 Likes
0
1766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:45 AM . Last Modified: ‎2024-03-12 03:24 AM

Have you tried different types of loads?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore