Hello All,
We currently have a couple UPS that when I go pull the plug on them to simulate a power outage it #1 does not email me and #2 does not log it.
I can remove the battery connection and it will log it and email me. I checked the settings and they are set to email and log for a power outage.
What am I missing.
Thanks
Kevin
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:43 AM . Last Modified: 2024-03-12 03:25 AM
It looks like you're configuration is default - like you haven't disabled any events after adding recipients?
And also, yes, the event log is not helpful since it has not been cleared. I would like to see it after Monday or after you can simulate a power outage perhaps? I see nothing strange as to why emails would not be coming through.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:43 AM . Last Modified: 2024-03-12 03:25 AM
Hi Kevin,
Are you utilizing PowerChute Business Edition or a UPS Network Management Card?
If it is a UPS Network Management Card, can you provide me the log files from it please for review (config.ini, event.txt, and data.txt)? Instructions here -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:43 AM . Last Modified: 2024-03-12 03:25 AM
We use network management cards in all the UPS's from APC. The other night after hours I VPN into our system and webbed into the interface I then did a reset/reboot of the management interface. I am standing here at the unit now. when I unplug it and plug it back in it does now send and email and logs the outage. I need to go to the other site and verify that one also works after a reset.
Thanks
Kevin
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:43 AM . Last Modified: 2024-03-12 03:25 AM
Oh, ok. Well let me know if you still have a problem and if you can provide the logs to look at and specify what timeframe to look at.
Did you see anything in the network management card log like "UPS: Lost UPS to NMC communication" or similar prior to your reset?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:43 AM . Last Modified: 2024-03-12 03:25 AM
Still having the same issue at the other location. I attached the files you asked for. I recently cleared the logs so do not know if they will help you out any. Every Monday morning all our Generators do a test run and switch power 2 times between 5am and 6am. that is when the UPS will see the outage.This is when I noticed we were not getting the email from 2 of the many UPS's we have in our system.
Thanks
Kevin
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:43 AM . Last Modified: 2024-03-12 03:25 AM
It looks like you're configuration is default - like you haven't disabled any events after adding recipients?
And also, yes, the event log is not helpful since it has not been cleared. I would like to see it after Monday or after you can simulate a power outage perhaps? I see nothing strange as to why emails would not be coming through.
Link copied. Please paste this link to share this article on your social media post.