Smart UPS-2200RM not logging power outage
Hello All,
We currently have a couple UPS that when I go pull the plug on them to simulate a power outage it #1 does not email me and #2 does not log it.
I can remove the battery connection and it will log it and email me. I checked the settings and they are set to email and log for a power outage.
What am I missing.
Thanks
Kevin
- Labels:
-
Smart-UPS & Symmetra LX | RM
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:43 AM . Last Modified: 2024-03-12 03:25 AM
It looks like you're configuration is default - like you haven't disabled any events after adding recipients?
And also, yes, the event log is not helpful since it has not been cleared. I would like to see it after Monday or after you can simulate a power outage perhaps? I see nothing strange as to why emails would not be coming through.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:43 AM . Last Modified: 2024-03-12 03:25 AM
Hi Kevin,
Are you utilizing PowerChute Business Edition or a UPS Network Management Card?
If it is a UPS Network Management Card, can you provide me the log files from it please for review (config.ini, event.txt, and data.txt)? Instructions here -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:43 AM . Last Modified: 2024-03-12 03:25 AM
We use network management cards in all the UPS's from APC. The other night after hours I VPN into our system and webbed into the interface I then did a reset/reboot of the management interface. I am standing here at the unit now. when I unplug it and plug it back in it does now send and email and logs the outage. I need to go to the other site and verify that one also works after a reset.
Thanks
Kevin
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:43 AM . Last Modified: 2024-03-12 03:25 AM
Oh, ok. Well let me know if you still have a problem and if you can provide the logs to look at and specify what timeframe to look at.
Did you see anything in the network management card log like "UPS: Lost UPS to NMC communication" or similar prior to your reset?
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:43 AM . Last Modified: 2024-03-12 03:25 AM
Still having the same issue at the other location. I attached the files you asked for. I recently cleared the logs so do not know if they will help you out any. Every Monday morning all our Generators do a test run and switch power 2 times between 5am and 6am. that is when the UPS will see the outage.This is when I noticed we were not getting the email from 2 of the many UPS's we have in our system.
Thanks
Kevin
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:43 AM . Last Modified: 2024-03-12 03:25 AM
It looks like you're configuration is default - like you haven't disabled any events after adding recipients?
And also, yes, the event log is not helpful since it has not been cleared. I would like to see it after Monday or after you can simulate a power outage perhaps? I see nothing strange as to why emails would not be coming through.