What does this mean - UPS: The output power is turned off

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • What does this mean - UPS: The output power is turned off
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:11 PM . Last Modified: ‎2024-03-01 12:07 AM

0 Likes
12
13894
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:11 PM . Last Modified: ‎2024-03-01 12:07 AM

What does this mean - UPS: The output power is turned off

There was a power issue on 7/9 and then on 7/12 the UPS output power is turned off.

What would cause this?

 

Portion of the log -

07/12/2015 09:53:52 UPS: The output power is now turned on.

07/12/2015 09:53:47 UPS: The output power is turned off.

07/09/2015 00:22:02 UPS: A discharged battery condition no longer exists.

07/09/2015 00:22:01 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.

Model: Smart-UPS 1400 RM XL

Serial Number: AS0941260801

Firmware Revision: 73.14.D

Manufacture Date: 10/06/09

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • off
  • output
  • power
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:12 PM . Last Modified: ‎2024-03-01 12:07 AM

0 Likes
0
13884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:12 PM . Last Modified: ‎2024-03-01 12:07 AM

Hi Randy,

Yes, v6.2.1 AOS (Operating System) and v6.2.1 for sumx application (for Smart-UPS and & Matrix UPS types) are the latest available if you found that on the website. Be advised it will be a completely different web UI, etc but has a lot more features, bug fixes, etc and you'll get more out of it.

If you need help upgrading, here is the knowledge base on doing that process and the available options -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156047 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:11 PM . Last Modified: ‎2024-03-01 12:07 AM

0 Likes
0
13884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:11 PM . Last Modified: ‎2024-03-01 12:07 AM

Hi,

Can you provide the full event.txt and data.txt? http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156131 provides instructions in retrieving the full logs.

Output power turned off means the UPS output power has turned off and you have no power at the outlets on the back of your UPS.

I see battery related events there so depending on how high your load is, how old your battery is, and how long the outage is, it could also mean you need a new battery soon - which may be a separate issue from why the output power turned off on the 12th.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:11 PM . Last Modified: ‎2024-03-01 12:07 AM

0 Likes
0
13884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:11 PM . Last Modified: ‎2024-03-01 12:07 AM

Thank you for the reply. 

the Battery events were from July 9 and cleared July 9.  The Output power is turned off is the only event listed on July 12.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:11 PM . Last Modified: ‎2024-03-01 12:07 AM

0 Likes
0
13884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:11 PM . Last Modified: ‎2024-03-01 12:07 AM

Hi Randy,

Can you attach the full files? We might find this happened previously in a similar sequence or we had a UPS fault some time ago. I am also interested to see what is in the data log around the same time on the 12th.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:12 PM . Last Modified: ‎2024-03-01 12:07 AM

0 Likes
0
13884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:12 PM . Last Modified: ‎2024-03-01 12:07 AM

Hi Angela,

 

Can you help me retrieve those files?  I used this info link but still unable to pull the files.

http://www.schneider-electric.us/sites/us/en/support/faq/faq_main.page?page=content&country=ITB〈=en&...

American Power Conversion               Network Management Card AOS      v5.0.3
(c) Copyright 2009 All Rights Reserved  Smart-UPS & Matrix-UPS APP       v5.0.3

apc>dir
E000: Success
drwxrwxrwx  1 apc      apc            0 Sep 11 2009 ./
drwxrwxrwx  1 apc      apc            0 Sep 11 2009 ../
--w--w--w-  1 apc      apc        47104 Jul 15 2015 event.txt
--w--w--w-  1 apc      apc        20480 Jul 15 2015 data.txt
--w--w--w-  1 apc      apc            1 Sep 11 2009 dlogmask

apc>logzip
E101: Command Not Found

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:12 PM . Last Modified: ‎2024-03-01 12:07 AM

0 Likes
0
13884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:12 PM . Last Modified: ‎2024-03-01 12:07 AM

Hi Randy,

Ok, so you have 5.0.3 firmware I see which is really, really old and does not support the logzip command (which is used with v5.X.X or higher). Not part of your original question but when we're done, you may want to consider upgrading the Network Management Card firmware.

You'll want to follow the FTP instructions and connected via an FTP utility or through Windows command prompt FTP and retrieve the event.txt and data.txt files. Refer to the first section under Resolution called "File Transfer Protocol - All Network Management Cards or Web/SNMP Card" and follow those instructions.

Let me know if you still get stuck. Worst case, go to the web interface and go to Logs tab and choose "Launch Log in New Window" for both event and data logs and PDF what you get for me to view.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:12 PM . Last Modified: ‎2024-03-01 12:07 AM

0 Likes
0
13884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:12 PM . Last Modified: ‎2024-03-01 12:07 AM

Hi Angela,

Thank you for the information but I still wasn't able to use the FTP sequence.  I copied the eventlog from CLI and attached to this posting.   Thanks again.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:12 PM . Last Modified: ‎2024-03-01 12:07 AM

0 Likes
0
13884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:12 PM . Last Modified: ‎2024-03-01 12:07 AM

Ok, thanks - better than nothing 🙂

I see according to the date/time of January 2014, you had some battery issues and faults that cleared up - can you confirm to me if you replaced the batteries then or if the faults cleared up on their own and the battery was not replaced then? If not, do you know how old the battery in this UPS is? The manufacture date of the UPS is 2009 so if the original battery is still present, it'd be about 6 years old now and would make sense that you're receiving those types of messages in the log.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:12 PM . Last Modified: ‎2024-03-01 12:07 AM

0 Likes
0
13884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:12 PM . Last Modified: ‎2024-03-01 12:07 AM

I'm not sure if the batteries were ever replaced, I looked through the history for this location and didn't find anything on the UPS.  Would a battery issue cause the OUTPUT power to turn off at random times?  According to my site contact, there have been no power issues (outages) since July 9.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:12 PM . Last Modified: ‎2024-03-01 12:07 AM

0 Likes
0
13884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:12 PM . Last Modified: ‎2024-03-01 12:07 AM

This could be related to a battery. What happens if you run a self test now? There could be power blips happening so fast that the events being logged for 1 second or less outages or something may not be recorded beyond the output power turning on and off as you see in the log.

Furthermore, logging may be better if you consider updating the firmware on the Network Management Card itself.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:12 PM . Last Modified: ‎2024-03-01 12:07 AM

0 Likes
0
13884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:12 PM . Last Modified: ‎2024-03-01 12:07 AM

What is the latest FW version (v6.2.1?) and can the previous versions be skipped?

 

Hardware Factory
---------------
Model Number:           AP9630
Serial Number:          BA0937030419
Hardware Revision:      05
Manufacture Date:       09/11/2009
MAC Address:            00 C0 B7 4E 14 B5
Management Uptime:      6 Days 15 Hours 58 Minutes

Application Module
---------------
Name:                   sumx
Version:                v5.0.3
Date:                   Aug  6 2009
Time:                   21:53:59

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:12 PM . Last Modified: ‎2024-03-01 12:07 AM

0 Likes
0
13885
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:12 PM . Last Modified: ‎2024-03-01 12:07 AM

Hi Randy,

Yes, v6.2.1 AOS (Operating System) and v6.2.1 for sumx application (for Smart-UPS and & Matrix UPS types) are the latest available if you found that on the website. Be advised it will be a completely different web UI, etc but has a lot more features, bug fixes, etc and you'll get more out of it.

If you need help upgrading, here is the knowledge base on doing that process and the available options -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156047 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:12 PM . Last Modified: ‎2024-03-01 12:07 AM

0 Likes
0
13884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:12 PM . Last Modified: ‎2024-03-01 12:07 AM

Because of this note in FA167693 -

v5.0.X->v6.X.X upgrade path will cause a loss of TCP/IP settings. You can avoid this by going v5.0.X->v5.1.X->v6.X.X

I think I will just have the UPS replaced. 

Thank you for your assistance.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore