One of my units (an S20 BLK) often reports an Undervoltage condition. Here's its current Overview NMC screen:

As you can see, the input voltage is 115V. Here's what the Configuration/Power screen looks like:

Does the NMC use the values in this screen to determine how it defines an under/over-voltage situation? If so, I'm guessing some combination of the 100VAC Low Transfer Voltage setting and the "High" Sensitivity setting is telling the UPS to treat 115VAC as an under-voltage condition, but how is that being calculated?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:12 AM . Last Modified: 2024-03-12 11:53 PM
Hi stevejenkins
This UPS has automatic voltage regulation (AVR) inside. Here is what I found out:
Low Voltage Cutoff (Upward, Downward) 106, 100 VAC
Double Boost to Single Boost (upward, downward) 110, 106 VAC
Single Boost - On Line (Upward, Downward) 117, 113 VAC
On Line - Trim (Upward, Downward) 126,122
High Voltage Cutoff - Trim to battery (Upward, Downward) 134, 130
So single boost in Highest threshold will be 117vac, 115vac Medium and 113vac low. Seems like it's boosting your voltage since its at 115 cause the thresholds are fairly tight.
If you're concerned, we can lower the voltage transfer ranges a few notches which also affects the AVR transfer ranges.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:12 AM . Last Modified: 2024-03-12 11:53 PM
Hi stevejenkins
This UPS has automatic voltage regulation (AVR) inside. Here is what I found out:
Low Voltage Cutoff (Upward, Downward) 106, 100 VAC
Double Boost to Single Boost (upward, downward) 110, 106 VAC
Single Boost - On Line (Upward, Downward) 117, 113 VAC
On Line - Trim (Upward, Downward) 126,122
High Voltage Cutoff - Trim to battery (Upward, Downward) 134, 130
So single boost in Highest threshold will be 117vac, 115vac Medium and 113vac low. Seems like it's boosting your voltage since its at 115 cause the thresholds are fairly tight.
If you're concerned, we can lower the voltage transfer ranges a few notches which also affects the AVR transfer ranges.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:12 AM . Last Modified: 2024-03-12 11:53 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:12 AM . Last Modified: 2024-03-12 11:53 PM
Awesome, Angela. Those ranges are helpful data (bookmarking thread... NOW). I'm actually OK having the thresholds tight. This is powering an Xbox, a PS3, and AppleTV, a Plasma TV, and a high-end AV Receiver, so a tight range is fine by me to protect all that AV equipment. ![]()
Just for my geekiness, based on what you said, am I right in understanding the following?
If #2 is correct, is there a "fixed" mathematical relationship between the Voltage Transfer values and each of the AVR levels you stated? Meaning, are the AVR trim settings some percentage of the voltages shown on the UPS/Power tab? If so, how are those calculated (what's the percentage)?
Thx!
Steve
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:12 AM . Last Modified: 2024-03-12 11:53 PM
Yes, you're correct. 14.6% is the percentage.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:12 AM . Last Modified: 2024-03-12 11:53 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:12 AM . Last Modified: 2024-03-12 11:53 PM
Awesome. 14.6, huh? Nothing like a nice round number. ![]()