Weird charging behavior on new SMT1500C

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Weird charging behavior on new SMT1500C
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
MysteryGuy_apc
Ensign MysteryGuy_apc
Ensign

Posted: ‎2022-02-17 07:49 AM

0 Likes
1
1362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-17 07:49 AM

Weird charging behavior on new SMT1500C

Hi;

 

I just got a brand new SMT1500C and it seems to be showing some strange behavior.

 

I already had an SMT1500 and the charging behavior of the SMT1500C seems very different (and seemingly wrong).

 

I wanted to know if this is how the SMT1500C's are supposed to behave or if I might have a defective one.

 

I installed PCBE 10.0.5 on Windows 10. I'm using the USB cable connection  to monitor the UPS status.

 

When I first started up the SMT1500C it reported a charge of about 8x% and voltage of 27.3 V.

 

After about 70 minutes it reported 96% charge/ 27.3 V. (This is with a light load of about 15%).

 

But progress crawled after that and it took about 22 more hours for the charge to finally report 100%. It slowly added 0.1% at a time maybe every 30-60 minutes.

 

After reaching 100% the reported battery voltage dropped from 27.2V to around 26.7 volts over the course of about 20-30 minutes.

 

I decided to initiate a 'self-test' at that point which seemed to work. The reported charge/voltage dropped to about 98.8 % charged / 27.2 V.

 

15 hours or so later it finally reports 100% charge again (making slow 0.1% increments along the way like before).

 

The reported battery voltage has dropped to 26.7V over the course of about 50 minutes since reaching 100%.

 

On my old SMT1500,

 

1) It never takes that long after a self test to reach 100% charge.  I think the last

    runtime calibration (with a much longer drain time) reported return to 100% within 2-3

    hours.

 

2) I don't think I've ever seen my SMT1500 report a voltage lower than about 27.2V

    after reaching 100% charge.

 

    Is it right for the battery voltage to drop on the SMT1500C after reaching 100%

    charge?

 

It seems to me that something is wrong if it takes so very long to report 100% charge after even a self-test.

 

Thanks;

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
MysteryGuy_apc
Ensign MysteryGuy_apc
Ensign

Posted: ‎2022-02-20 09:59 AM . Last Modified: ‎2022-02-20 10:20 AM

0 Likes
0
1343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-20 09:59 AM . Last Modified: ‎2022-02-20 10:20 AM

I was hoping someone who has an SMT1500C could at least relate how their device compares for recovery from Self-test, and battery voltage at 100% charge.

 

At any rate, I've returned my new UPS since it unexpectedly dropped it's load output twice. 

 

Once momentarily when sliding the battery back in after I examined it (to see if it showed any obvious issues).

 

Then later half-way through recharging after a run-time calibration when I tried to move the unit back a few  inches.

 

So my unit apparently had something very wrong with it.

 

My system is  back on an old SU1400BX120 (from Jan. 2000) I was planning on replacing (purely because of age). Now things are once again normal.

 

It may be a while before I get a replacement, so I will have to see how the SMT1500C  charging behavior is then (compared to an SMT1500).

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore