Web UI timeout too short

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Web UI timeout too short
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 12:38 AM . Last Modified: ‎2024-02-29 11:08 PM

0 Likes
4
5940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:38 AM . Last Modified: ‎2024-02-29 11:08 PM

Web UI timeout too short

On all the web UI's for APC devices I have seen so far, the maximum idle time before auto-logoff is 10 minutes.

This drives me nuts. Not only is "security by obscurity" not particularly useful (especially if the session is already running over SSL/TLS), the glacial performance of the webserver in the APC cards means that every time I get auto logged-off on a device while I'm busy doing something else that is part of the same task and have to log back on, it takes an interminable time to get the management interface back up again.

I don't mind if you make some silly short timeout the default setting, but can you please offer some longer options for when we're multitasking and can't always get back to that page in time to avoid an auto-logoff?

(I have browsers that can be set to auto-reload pages but this is a PITA to have to do every time I touch an APC device)

Thanks.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • card
  • logoff
  • management
  • timeout
  • ui
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

0 Likes
0
5934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

For the events and actions, I find it is a lot easier to FTP the config.ini file from the device, make mass edits using a text processor (cutting out all but the event section) and then FTP it back to the device. The only "gotcha" is that if you have alerts for configuration changes enabled, you will get an alert for every item that changes (but you'd also get that if you changed them one at a time via the web interface).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:38 AM . Last Modified: ‎2024-02-29 11:07 PM

0 Likes
0
5934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:38 AM . Last Modified: ‎2024-02-29 11:07 PM

Hi Phil,

Based on your comment about glacial speed using SSL/TLS, I assume you're talking about the older AP9617/18/19 cards? If so, these likely won't be updated to support longer than 10 minutes.

On v6.X.X firmware for AP9630/31/35 Network Management Card 2, user sessions work differently and now on a per user basis, you can now set this to a maximum of 60 minutes. (The default is still 10 minutes.) We also offer multiple users logged in at a time as well on that newer firmware platform. 

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-08 12:38 AM . Last Modified: ‎2024-02-29 11:07 PM

0 Likes
0
5934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:38 AM . Last Modified: ‎2024-02-29 11:07 PM

Those older cards only supported a single log-in, which could be a problem if you lose your session! The short timeout makes the session available again. Things are much better on the newer cards with multiple sessions and longer timeouts that Angela mentions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:38 AM . Last Modified: ‎2024-02-29 11:07 PM

0 Likes
0
5934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:38 AM . Last Modified: ‎2024-02-29 11:07 PM

Yes, the older cards are what I have in my sites so far. (The last time I updated some hardware at a client site [this week] it was formerly using a 9619 linked with a custom temperature control device I had built around it, and I did not feel like billing to re-design and test that whole mechanism again just because the UPS went bad. So the new UPS went somewhere else and I used an older one and the 9619 card to keep all that working.)

However I did try your "test drive" page for the 963x cards the other day and I think I see what happened. I wanted to look at the environmental monitoring aspects and the 9631 page was basically dead (you may want to look into that, it's still that way today), so I went to the "UPS NMC with Environmental Monitoring & Out of Band Management" page - but it appears to be running a 9618 rather than a 9635. I had also looked at one of the dedicated environmental monitoring device's test drive page [http://159.215.9.66/] - same issues/older firmware. (I also did look at the 9630 page as well and saw the new UI, but didn't check the session timeout on it. I just looked again and found the new 60-min session timeout setting, thanks.)

Re: the overall interface performance - while it's certainly snappier than the 961x's and the other management UI's on your testdrive page, considering it's only running HTTP it was hard to accurately assess. So I'll take your word on that. 😉

PS: One other issue, while on the subject of the mgmt card UI - which looks very similar in this respect in the 963x cards - is in the event action page. It takes a ridiculously long time, IMHO, to configure those things because you have to drill down page-by-page into each subset of those events and actions, and then back-back-back to the beginning each time to adjust another one, and there is little "situational awareness" of what you end up with because there is no grid or matrix where you can view all the events/actions on one page and see which ones are eg set to non-default settings and what they are. So my wish list would include some sort of matrix with tickboxes where I can adjust a bunch of those at the same time and see them all in columns showing which are changed from defaults etc. Would save a huge amount of time if you're doing a lot of customization.

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

0 Likes
0
5935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

For the events and actions, I find it is a lot easier to FTP the config.ini file from the device, make mass edits using a text processor (cutting out all but the event section) and then FTP it back to the device. The only "gotcha" is that if you have alerts for configuration changes enabled, you will get an alert for every item that changes (but you'd also get that if you changed them one at a time via the web interface).

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of