does email nmc notifications work with group emails

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • does email nmc notifications work with group emails
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

0 Likes
11
2496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

does email nmc notifications work with group emails

i have 2 40kva UPS that am looking after and another 30kva in a remote place. i have email notifications configured quite well but the provision for email only goes up to 4 email addresses. Because of this limitation on the number of email notifications recipients, my colleague created a group email which comprises of more than 7 recipients but the sad part is that the group email doesnt get the notifications. when i just put 4 ordinary emails as recipients, it works ok. Is anyone able to resolve this email recipient limitation

Secondly;

i also have a 16kva symmetra power array which is in bypass, i tried to access the nmc while the UPS is in bypass but the card was not responding. Does this mean the network management card can only be configured while the symmetra power array is online?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

0 Likes
0
2496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

Thanks so much for sharing Jon.

The firmware you referenced is for the UPS itself. You'll want to find the Network Management Card firmware. If it is a blue and white interface it is older and if it is a newer management card and firmware, it will be green and white. AP9617/18/19 management cards are older and do not support email authentication but AP9630/31/35 do and should meet the requirements for working with your server using SMTP authentication (I hope).

Let me know if you have any questions. We could explore a firmware update if you do have an AP9630 or AP9631 if you prefer not to change this setting on your mail server.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

0 Likes
0
2496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

Hi,

Yes, most, if not all management cards have a (4) recipient limit for email. (I say that now in case a future firmware changes something.) The NMC can't tell what recipient you're sending it to and if it is a group or not. That being said, the only solution would be to create a group on your email server and have the email server forward it to the recipients of that group. If it is not working, my first suspicion would be on the configuration of the group server side or the configuration of that recipient on the management card. If the configuration of that group is the same as the other (3) recipients on the management card, I'd look at the mail server logs to see if you can verify if the management card is sending the email and if there is an error some place else.

Regarding your second question, an NMC is accessible over the network as long as the UPS electronics are energized. The state of the UPS output does not matter - bypass, on, off, etc. If your access is changing based on UPS state, I'd validate the network connection to the UPS is not dependent on the UPS state some how - for example, a switch that isn't powered by the UPS and goes off during a bypass or off state for some reason. You could also validate the LEDs on the management card visually when the UPS is in bypass. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

0 Likes
0
2496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

Thank you for the reply angela, unfortunately it hasnt worked out. The group email still not receiving any notification.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

0 Likes
0
2496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

Can you confirm - what doesn't work? Both the email test function and notifications or just the test or just the notifications?

Could you share your event.txt and config.ini from this device for review? (Instructions on downloading log files are here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156131)

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

0 Likes
0
2496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

The test email doesnt work with the created group email but works well with other ordinary emails.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

0 Likes
0
2496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

Can you provide further detail please? Error message during test, log files, etc?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

0 Likes
0
2496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

Thank you Angela, a test email is always a success via the NMC but the email doesnt reach the recipient. It doesnt bring any error

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

0 Likes
0
2496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

Hi Katongo,

So how do we know this is a failure with the NMC versus a failure with the mail server/group configuration somewhere? Can you confirm your mail server is recieving a connection or an email from the NMC?

I don't see how if the NMC is not displaying an error that the issue can be on the NMC side. The NMC has no ability to tell if the recipient is a group or a single individual account and the fact that there is no error, makes me think that you should look into the mail server log or group configuration.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

0 Likes
0
2496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

Thank you angela, i think will leave puzzle with my coleague managing the servers. 

its only that (zesco) the electricity company i work for thought. the problem was with my UPS units.

On a different scenarior, i have smart UPS VT 40Kva with model number SUVTP40KH. what replacement parts can i buy for this machine? The people in your sales department are asking for part numbers which i dont know where to find. Can we use the model number to determine the part numbers?

The task i have at work is to provide a list of replacement parts which can be kept in our stores for the SUVTP40KH.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

0 Likes
0
2496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

I see you already posted this Smart-UPS VT question in another thread but your local technical support team may be able to provide you a list. For the larger, more complex UPSs that are used in different configurations and regions, we aren't able to provide that type of detail here unfortunately.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

0 Likes
0
2496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

I know this is an old post but I ran into the same problem.  I created a distribution group in Exchange 2007.  When sending test emails, they would go to my email address fine but emails sent to the group would never go through.  The NMC reported all tests as successful.

The problem in my case turned out to be that the new group I created had a security setting enabled.  In the Distribution Group properties in the Exhange Management Console, under Mail Flow Settings > Message Delivery Restrictions, the checkbox for "Require All Senders are Authenticated" was checked.  We are running firmware 319.11.d (version might not be correct) and as of that version, it's not possible to supply login credentials for the email server. I don't believe this setting used to be enabled for distribution groups by default, but possibly a MS patch changed that. Not sure.

We have a special email server that doesn't require login but restricts sending based on sender IP. We use this for the UPS and other devices such as multifunction printers that either can't supply credentials or still don't work when we do.

The downside of disabling authentication is you run the risk of a spammer getting the group address and spamming it, but in my experience with over 500 DGs where I work, it's extremely rare.  If it becomes a problem, I'll just block email to that group on our hosted anti-spam service.

So:

1) Make sure your UPS IP is allowed to relay on your mail server.

2) Make sure sending to the group doesn't require authentication.

3) Optionally, "Hide Group from Exchange Address Lists"

  • Tags:
  • card
  • email
  • group
  • management
  • network
  • NMC
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

0 Likes
0
2497
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

Thanks so much for sharing Jon.

The firmware you referenced is for the UPS itself. You'll want to find the Network Management Card firmware. If it is a blue and white interface it is older and if it is a newer management card and firmware, it will be green and white. AP9617/18/19 management cards are older and do not support email authentication but AP9630/31/35 do and should meet the requirements for working with your server using SMTP authentication (I hope).

Let me know if you have any questions. We could explore a firmware update if you do have an AP9630 or AP9631 if you prefer not to change this setting on your mail server.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore