Very low runtime on low load UPS compared to similar model with high load

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Very low runtime on low load UPS compared to similar model with high load
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:56 PM . Last Modified: ‎2024-03-07 12:06 AM

0 Likes
1
1429
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:56 PM . Last Modified: ‎2024-03-07 12:06 AM

Very low runtime on low load UPS compared to similar model with high load

Hi, I have two similar model, one slightly newer than the other Smart-UPS 750's, with NMC2 cards.

This morning we had a short power failure, and one UPS lasted less than 6 minutes, the other the entire outage.

Weird thing is the UPS that ran out of power has much less load..

This is from the two UPS's:

Battery Temperature
33.7°C
Runtime Remaining
5min
UPS Input
Input Voltage
114.4 VAC @ 60.0 Hz
UPS Output
Output Voltage
114.4 VAC @ 60.0 Hz
Load Current
0.7 Amps
Output VA
9.7 %
Output Watts
7.8 %
Output Efficiency
79.0 %
Output Energy Usage
2081.38 kWh
Battery Status
State of Charge
100.0 %
Battery Voltage
27.0 VDC
Next Battery Replacement Date
06/24/2021

Battery Temperature
32.8°C
Runtime Remaining
28min
UPS Input
Input Voltage
113.0 VAC @ 60.0 Hz
UPS Output
Output Voltage
113.0 VAC @ 60.0 Hz
Load Current
1.8 Amps
Output VA
27.9 %
Output Watts
37.0 %
Output Efficiency
95.0 %
Output Energy Usage
3629.90 kWh
Battery Status
State of Charge
100.0 %
Battery Voltage
27.1 VDC
Next Battery Replacement Date
04/04/2043

Notice the 28mins vs 5mins runtime, and yes I see the efficiency is 95% vs. 79%, but the load is 1.7A vs. only 0.7A.

How is it possible that the 1.7A draw will last 5 times longer than the 0.7A draw?

The UPS's are scheduled to self-test every two weeks, no errors reported.

I ran a manual self-test on the bad UPS, and the test passed, but the battery failed.

How is it possible for the test to pass but clearly the battery failed?

10/11/2016 18:07:06 Device UPS: A low battery condition no longer exists.
10/11/2016 18:07:06 Device UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
10/11/2016 18:07:05 Device UPS: Self-Test passed.
10/11/2016 18:06:59 Device UPS: A discharged battery condition no longer exists.
10/11/2016 18:06:59 Device UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
10/11/2016 18:06:58 Device UPS: Self-Test started by management device.
10/11/2016 18:06:56 Device UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.

Bad battery?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:56 PM . Last Modified: ‎2024-03-07 12:06 AM

0 Likes
0
1429
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:56 PM . Last Modified: ‎2024-03-07 12:06 AM

I replaced the battery, and runtime is back to normal.

Seems to me that the battery test is not doing its job.

APC, how about it, logs clearly shows dead battery during test, but battery test passes?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:56 PM . Last Modified: ‎2024-03-07 12:06 AM

0 Likes
0
1430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:56 PM . Last Modified: ‎2024-03-07 12:06 AM

I replaced the battery, and runtime is back to normal.

Seems to me that the battery test is not doing its job.

APC, how about it, logs clearly shows dead battery during test, but battery test passes?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore