Using USB to RS232 to connect SC 450VA to a QNAP

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Using USB to RS232 to connect SC 450VA to a QNAP
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:43 AM . Last Modified: ‎2024-03-15 05:50 AM

0 Likes
2
1856
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:43 AM . Last Modified: ‎2024-03-15 05:50 AM

Using USB to RS232 to connect SC 450VA to a QNAP

Using USB to RS232 adapter to connect SC 450VA to a QNAP?

Not sure in which section post this, my issue is the next:

My company owns a UPS 450VA which comes with a RS232 port as only communication port, and a QNAP TS-453BU-RP-4G

Does make sense to use an USB to RS232 adaptor in order to get the auto-protection running in the QNAP?
There is any other solution? Any technical spec for the Adapter?

Thanks.
APC Smart-UPS SC 450VA 230V
https://www.apc.com/shop/id/en/products/APC-Smart-UPS-SC-450VA-230V-1U-Rackmount-Tower/P-SC450RMI1U 

USB to RS232 adapter on Amazon.de
https://www.amazon.de/dp/B00QUZY4UG/ref=sr_1_3?keywords=USB+RS232&qid=1575449525&sr=8-3

xYrIkaIOVymbM8oLa3liKA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngxYrIkaIOVymbM8oLa3liKA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png
Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • adapter
  • auto-protection
  • qnap
  • rs232
  • usb-serial
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:43 AM . Last Modified: ‎2024-03-15 05:50 AM

0 Likes
0
1856
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:43 AM . Last Modified: ‎2024-03-15 05:50 AM

Hello,

I recommend you get a UPS that offers USB support. Even with a USB to serial converter the UPS will not communicate with the USB on the QNAP. The converter cable is designed to create a serial port not convert serial to USB. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:43 AM . Last Modified: ‎2024-03-15 05:50 AM

0 Likes
0
1857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:43 AM . Last Modified: ‎2024-03-15 05:50 AM

Hello,

I recommend you get a UPS that offers USB support. Even with a USB to serial converter the UPS will not communicate with the USB on the QNAP. The converter cable is designed to create a serial port not convert serial to USB. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Manius
Manius
Cadet

Posted: ‎2025-09-17 08:53 AM

0 Likes
0
398
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-17 08:53 AM

In case other friends run into this as well, here are my two cents:

1. ssh into QNAP and manually install "apcupsd", then manually install NUT server, the flow is: connect APC  smart ups with QNAP through DB9-USB convertor, and config apcupsd so it will recognize the existance of the Smart UPS, the NUT server is used to convert the information obtained through apcupsd into a standard NUT output format, and in QNAP ups selection panel, use the 3rd option "Network UPS slave", but in fact the "Network master" is exactly the QNAP itself. In this way you let your QNAP listen to your APC Smart UPS through the standard NUT protocol, but the NUT server is set up on QNAP itself, and NUT in turn obtains UPS parameters from your serial-ported UPS through DB9-USB convertor, so you have your APC Smart UPS work tightly with your QNAP.

 

I personally wouldn't recommend this way, because it's way too intrusive for the QNAP system, too much low-level manipulations thus hard to maintain.

 

2. the second solution will be: connect APC Smart UPS to another Linux box, or Windows server, whatever. and set up NUT server there, on QNAP side it will be almost the same: select "Network UPS slave" mode, and listen to the NUT server from you another Linux box, which is what I'm doing now.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore