Using 2 NAS boxes from one UPS (SMT750IC)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Using 2 NAS boxes from one UPS (SMT750IC)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 04:51 AM . Last Modified: ‎2024-03-08 03:59 AM

0 Likes
1
1166
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:51 AM . Last Modified: ‎2024-03-08 03:59 AM

Using 2 NAS boxes from one UPS (SMT750IC)

Hi all,

  I have just bought an APC SMT750IC UPS and my original goal was to have it connected and run 2 NAS boxes. The NAS I own are a QNAP TVS-951-X and an old Netgear ReadyNAS Ultra. The QNAP holds all my data and any critical data gets backed up to the Netgear NAS. My original goal was to have my UPS send the shutdown to both NAS in the event of power failure.

  I have tried connecting the USB to the QNAP and enabling the Network UPS Master and putting the internal IP of the Netgear NAS in here. However, when testing this setup the QNAP powers off but the ReadyNAS remained on-line.

  I tried connecting the USB to the Readynas and tried to set-up that up as the UPS master host but again that failed. The ReadyNAS shutdown but the QNAP stayed on-line

I have tried to put a USB HUB in the back of the UPS and connect both NAS but after a bit of reading I found out that USB hubs only have 1 upstream and it doesn't work

  My ask is has anyone tried this setup of 1 up to 2 NAS boxes and got it working and if so what am I missing.

Thanks

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 04:51 AM . Last Modified: ‎2024-03-08 03:59 AM

0 Likes
0
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:51 AM . Last Modified: ‎2024-03-08 03:59 AM

So I have been back at this problem again today and I have been reading some more posts on other forums. I have tried to edit the upsmon.conf file on the Readynas box so the MONITOR line now reads:

MONITOR qnapups@ admin 123456 slave

I have also modified the upsd.users on the readynas to look like the following:

[admin]
password = 123456
allowfrom =
upsmon slave

However, when I set up the QNAP as the UPS master and try to set the Readynas as the slave I still get the same error Could not connect to the specified UPS server. Please verify that UPS sharing is enabled on that system and try again.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Anonymous user
Not applicable

Posted: ‎2021-06-30 04:51 AM . Last Modified: ‎2024-03-08 03:59 AM

0 Likes
0
1166
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:51 AM . Last Modified: ‎2024-03-08 03:59 AM

So I have been back at this problem again today and I have been reading some more posts on other forums. I have tried to edit the upsmon.conf file on the Readynas box so the MONITOR line now reads:

MONITOR qnapups@ admin 123456 slave

I have also modified the upsd.users on the readynas to look like the following:

[admin]
password = 123456
allowfrom =
upsmon slave

However, when I set up the QNAP as the UPS master and try to set the Readynas as the slave I still get the same error Could not connect to the specified UPS server. Please verify that UPS sharing is enabled on that system and try again.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore