Redundant Power Supplies

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Redundant Power Supplies
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 04:51 AM . Last Modified: ‎2024-03-08 04:00 AM

0 Likes
5
1369
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:51 AM . Last Modified: ‎2024-03-08 04:00 AM

Redundant Power Supplies

We have 2 servers that have redundant power supplies. We also have them each plugged into their own UPS. Is it a good idea to split the power between 2 UPS units? Like should I be plugging the power from server A into UPS A and UPS B and the same for server B? Currently server A is plugged into UPS A and server B is plugged into UPS B with the power split between the UPS units, how would I go about configuring Powerchute Business to know when both UPS units are on battery (in theory they'd be at the same time) and shut down when the runtime is low for both units combined?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:51 AM . Last Modified: ‎2024-03-08 04:00 AM

0 Likes
0
1369
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:51 AM . Last Modified: ‎2024-03-08 04:00 AM

it is a fine idea to do so. even better, is to make sure those two UPSs are on different circuits, so that if one circuit goes down, you still have a UPS that is online on a good circuit. if they arent on two different circuits, its still an ok idea, you just wouldnt have COMPLETE redundancy.

you can't do what you are looking for with powerchute business edition, unfortunately. a single PCBE agent cannot monitor multiple UPSs through powerchute business edition - you can only do it the other way around where the UPS shuts down multiple PCBE agents.

you CAN do what you are looking to do with a network management card and powerchute network shutdown software. you'd install the network management card in each UPS (which provides the same info/features as PCBE and even more) and then powerchute network shutdown on each server. you can configure powerchute network shutdown with a "custom install" and tell it to look at/monitor both network management cards via the network. it will only shutdown when it receives a shutdown command from both UPSs (and then also there are other certain conditions that it can shutdown with only a command from one UPS - such as lost communication, etc)

You can look at the different management cards here: [http://www.apc.com/products/family/index.cfm?id=98]

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:51 AM . Last Modified: ‎2024-03-08 04:00 AM

0 Likes
0
1369
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:51 AM . Last Modified: ‎2024-03-08 04:00 AM

so with one of these cards, and the network shutdown card
The network management card is a physical card you will install in the UPS smart slot and the powerchute network shutdown is actually software you will need to install on the two servers.

The cards dont REQUIRE a static IP, but if the IPs change, its going to be a pain to go back and edit the software to look at those new IPs. I dont recommend DHCP on anything in this set up because i can gurantee communication problems. i know for a fact that running DHCP on your servers with the powerchute network shutdown software, will cause a communication problem.

i recommend this configuration with the network management cards and powerchute network shutdown software because yeah, no need to worry about any cables besides an ethernet cable for the network management cards and then nothing besides installing the software on your servers, assuming they are already on the network.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:51 AM . Last Modified: ‎2024-03-08 04:00 AM

0 Likes
0
1370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:51 AM . Last Modified: ‎2024-03-08 04:00 AM

it is a fine idea to do so. even better, is to make sure those two UPSs are on different circuits, so that if one circuit goes down, you still have a UPS that is online on a good circuit. if they arent on two different circuits, its still an ok idea, you just wouldnt have COMPLETE redundancy.

you can't do what you are looking for with powerchute business edition, unfortunately. a single PCBE agent cannot monitor multiple UPSs through powerchute business edition - you can only do it the other way around where the UPS shuts down multiple PCBE agents.

you CAN do what you are looking to do with a network management card and powerchute network shutdown software. you'd install the network management card in each UPS (which provides the same info/features as PCBE and even more) and then powerchute network shutdown on each server. you can configure powerchute network shutdown with a "custom install" and tell it to look at/monitor both network management cards via the network. it will only shutdown when it receives a shutdown command from both UPSs (and then also there are other certain conditions that it can shutdown with only a command from one UPS - such as lost communication, etc)

You can look at the different management cards here: [http://www.apc.com/products/family/index.cfm?id=98]

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:51 AM . Last Modified: ‎2024-03-08 04:00 AM

0 Likes
0
1368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:51 AM . Last Modified: ‎2024-03-08 04:00 AM

so with one of these cards, and the network shutdown card, I could shutdown any servers that are connected to the UPS? I was looking at possibly acquiring the serial expansion cards to connect all of our servers to the UPS, but if the network shutdown can handle it, then that would save me having to do more cable management. Do these network management cards require a static IP?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:51 AM . Last Modified: ‎2024-03-08 04:00 AM

0 Likes
0
1368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:51 AM . Last Modified: ‎2024-03-08 04:00 AM

all 5 (or 7 if you count the two backups) server have static IP addresses. Of course I'll need to reconfigure our DHCP server to allow for more static IPS, was probably going to open up another 15 - 20 anyways as we are down to 2 free (we have kiosk type machines that are static, then 40 or 50 others that are DHCP) I think this will be good cause to install a switch inside the rack as opposed to having them on the wall.

Thank you so much for your help!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:51 AM . Last Modified: ‎2024-03-08 03:59 AM

0 Likes
0
1368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:51 AM . Last Modified: ‎2024-03-08 03:59 AM

no problem!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore