Unable to load webconsole

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Unable to load webconsole
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 12:43 AM . Last Modified: ‎2024-03-06 02:34 AM

0 Likes
3
1844
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:43 AM . Last Modified: ‎2024-03-06 02:34 AM

Unable to load webconsole

Dear All,

I have a APC SMART - UPS SC450 RM which im able to connect to this device via telnet fine, but unable to access this at all through a browser.

Have tried with port 80 in the browser and 443 and wondered if there was setting within the management card im missing. But i thought the webconsole we available by default.

Kind Regards

Geoff Edwards

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 12:43 AM . Last Modified: ‎2024-03-06 02:34 AM

0 Likes
0
1840
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:43 AM . Last Modified: ‎2024-03-06 02:34 AM

ok. this is a network management card but i am not aware of the fact you could use an NMC with this by default..anyways..

i'd do the following:

go to the Network menu- > Web/SSL/TLS menu -> and verify here that you see Access : Enabled and see if SSL/TLS is configured and on what ports. if access is disabled you can change the settings accordingly here and make sure you press the option for "accept changes" on each menu. the card needs to reboot to change this i think so you might need to ESC back to the main menu and log out and give it a few mins to reboot and try again.

if everything looks good there, i'd start by rebooting the NMC interface which will not affect the UPS in anyway by rebooting the load, incase you were wondering. this option is under Main Menu -> system menu -> Tools menu -> Reboot Management Interface. you'll have to type yes to confirm. log back in and verify you are trying to access it by the info on the Web/SSL/TLS menu.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 12:43 AM . Last Modified: ‎2024-03-06 02:34 AM

0 Likes
0
1840
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:43 AM . Last Modified: ‎2024-03-06 02:34 AM

can you provide a screenshot of what you see via telnet? i believe this unit only uses powerchute business edition and it does not have a telnet interface so that is why i am confused.

if it is powerchute business edition, you can try http on port 3052 and https on 6547

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 12:43 AM . Last Modified: ‎2024-03-06 02:34 AM

0 Likes
0
1840
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:43 AM . Last Modified: ‎2024-03-06 02:34 AM

Thanks for your quick response, we are using the Infrastruxure to administrate this box currently. I enclose the screenshot below as requested any advice you can give me would be much appreciated

Cheers

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 12:43 AM . Last Modified: ‎2024-03-06 02:34 AM

0 Likes
0
1841
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:43 AM . Last Modified: ‎2024-03-06 02:34 AM

ok. this is a network management card but i am not aware of the fact you could use an NMC with this by default..anyways..

i'd do the following:

go to the Network menu- > Web/SSL/TLS menu -> and verify here that you see Access : Enabled and see if SSL/TLS is configured and on what ports. if access is disabled you can change the settings accordingly here and make sure you press the option for "accept changes" on each menu. the card needs to reboot to change this i think so you might need to ESC back to the main menu and log out and give it a few mins to reboot and try again.

if everything looks good there, i'd start by rebooting the NMC interface which will not affect the UPS in anyway by rebooting the load, incase you were wondering. this option is under Main Menu -> system menu -> Tools menu -> Reboot Management Interface. you'll have to type yes to confirm. log back in and verify you are trying to access it by the info on the Web/SSL/TLS menu.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore