Hi,
I'm troubleshooting a sudden drop in SNMP data on an APC UPS for a customer. The client has two UPS of the same model, the other device is working without an issue. There are no issues with pinging the device.
Although the second UPS isn't reporting any issues and we're still receiving SNMP information on our monitoring software, I can't for the life of my access that device either through any of the following methods. So far I've determined the following:
- Unable to access the web interface using IP and ports 80, 443, 6547, 3052.
- Tried to access via Telnet or SSH, connection refused (I don't think this was ever enabled or set up).
- Ping is still responding fine without a problem.
- Confirmed IP hasn't been taken by another device by manually turning off the switch port to the UPS and it's still pingable.
I'm almost certain that the web interface port must have been changed to both devices (we normally leave it on the default 80), because it seems too coincidental that I can't access the UPS that's having issues nor the second UPS that's working normally. We have documentation on the UPS's user credentials, just not their web interface ports.
I'm trying to avoid going to the site and either reseating the NMC or factory resetting it. Hoping that there might be an expert that's come across this situation before.
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 06:07 AM . Last Modified: 2024-02-15 12:06 AM
Hi,
You should connect the serial cable to the card (SKU 940-0299) to the card. You will be able change the settings through the serial interface. I use Putty but any terminal emulator will work. The port speed should be set to 9600. Once logged in if you enter help you will see all of the command options. I suggest you look at the web settings first.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 06:07 AM . Last Modified: 2024-02-15 12:06 AM
Hi,
You should connect the serial cable to the card (SKU 940-0299) to the card. You will be able change the settings through the serial interface. I use Putty but any terminal emulator will work. The port speed should be set to 9600. Once logged in if you enter help you will see all of the command options. I suggest you look at the web settings first.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-06 12:51 PM
Bill,
This issue is similar to my current issue. I used to be able to log into my UPS (same model) through the web interface. Now it is telling me there is an error - connection aborted. I checked to make sure the IP address, user name and password are correct through Putty and all are okay. I am able to log in through putty, but have not idea how to check the web interface. The ? doesn't show any command related to web settings. I really don't want to reset the IP address if this is a browser issue. I am inside the network trying to reach a UPS on this internal network, so my firewall should not be blocking this.