UPS won't shutdown during a power failure

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS won't shutdown during a power failure
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 11:16 PM . Last Modified: ‎2024-03-06 03:21 AM

0 Likes
3
934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:16 PM . Last Modified: ‎2024-03-06 03:21 AM

UPS won't shutdown during a power failure

Hi,

I just noticed recently that my shutdown procedures are not working properly with my UPS. Model is a Smart-UPS 2200 RM XL with the network management card installed.

I have the low battery duration set for 5 minutes. The Shutdown delay is set to 5 minutes. So based on this, I thought that after 10 minutes the UPS would shut itself down and wait until the power has been restored (that is what it is set to under on-battery shutdown behaviour) to turn itself back on. So what ended up happening is I pulled the plug, the servers shutdown in the right amount of time but the UPS just kept going and almost drained the battery after 35 minutes. I couldn’t actually stick around to see what would happen when the battery would be drained. Am I missing some configuration settings in order to get the desired effect to happen?

Thanks

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • network_management_card
  • NMC
  • shutdown
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:16 PM . Last Modified: ‎2024-03-06 03:21 AM

0 Likes
0
934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:16 PM . Last Modified: ‎2024-03-06 03:21 AM

what is your total runtime?

what the low battery signaling time means is that when X amount of runtime is remaining, in your case 5 minutes, then initiate a low battery message to all of your PCNS clients, then the UPS will still be running on battery for those 5 minutes, then it will have an additional delay of 5 minutes.

what you should do is on your PCNS clients, on the last server to shutdown ONLY, configure the PCNS software to turn the UPS off after the client shuts down. so, when everything is shutdown, it will send a message to the UPS to turn off. I believe this is under Configure Shutdown on the PCNS web interface configuration.

by default, if you just install PCNS and don't do any configuration, it will shutdown based on that low battery duration as a "fail safe" method of notifying devices attached to shutdown because the UPS is running low on battery power.

hope that helps.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:16 PM . Last Modified: ‎2024-03-06 03:21 AM

0 Likes
0
935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:16 PM . Last Modified: ‎2024-03-06 03:21 AM

what is your total runtime?

what the low battery signaling time means is that when X amount of runtime is remaining, in your case 5 minutes, then initiate a low battery message to all of your PCNS clients, then the UPS will still be running on battery for those 5 minutes, then it will have an additional delay of 5 minutes.

what you should do is on your PCNS clients, on the last server to shutdown ONLY, configure the PCNS software to turn the UPS off after the client shuts down. so, when everything is shutdown, it will send a message to the UPS to turn off. I believe this is under Configure Shutdown on the PCNS web interface configuration.

by default, if you just install PCNS and don't do any configuration, it will shutdown based on that low battery duration as a "fail safe" method of notifying devices attached to shutdown because the UPS is running low on battery power.

hope that helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 11:16 PM . Last Modified: ‎2024-03-06 03:21 AM

0 Likes
0
935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:16 PM . Last Modified: ‎2024-03-06 03:21 AM

Thanks. That makes sense. I was misinterpreting the help file. Cheers.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 11:16 PM . Last Modified: ‎2024-03-06 03:21 AM

0 Likes
0
935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:16 PM . Last Modified: ‎2024-03-06 03:21 AM

I am wondering if others find this explanation makes sense?

I understand that Low Battery Duration is calculated as an amount left to run. The suggestion is made to "configure the PCNS software to turn the UPS off after the client shuts down. so, when everything is shutdown, it will send a message to the UPS to turn off." The PCNS agent runs under the operating system of the host server. Even under VMware that is essentially true although in that case its the hypervisor. Either way once the host has shut down, there is no longer any PCNS agent to send a message. So how can the PCNS software turn off the UPS after the client (the host) has shut down? Its no longer operating. It can't do anything.

I think a more likely explanation is that PCNS sends a message to the UPS/NMC just before it triggers OS shutdown (after would be too risky) telling it to shut down the UPS after a defined time interval. From other reading that interval is Low Battery Duration + Shutdown Delay.

I still don't understand how a UPS which has said "I have enough battery to run for Low Battery Duration" can run for that long and still run on for Shutdown Delay too. Perhaps that is a subject for another thread.

Message was edited by: ACMIitsupport

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of