UPS voltage settings

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS voltage settings
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-12 12:53 AM

0 Likes
3
10486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-12 12:53 AM

UPS voltage settings

Hi,

I have two SURT6000XLI ups with the following voltage configurations:

--------------------------------------------------------

- Output Voltage: 230vac

- Upper Bypass limit: 253vac

- Lower Bypass limit: 161vac

- Allowable Frequency range for UPS bypass: Auto sensing

- Power Quality Sensitivity: Automatic

--------------------------------------------------------

I can see that in the PowerChute Business Edition application that ihe input line voltage vary from 210vac to 228vac.

Since I am a total newbie to UPS power configuration, I need assistance to validate is this configuration (I assume factory default) is good enough to keep, or if it should be changed. The UPS's are currently supporting a bunch of Cisco networking equipment, HP storage and few HP servers.

Here is an example of what I have in my mind concerning a new configuration:

--------------------------------------------------------

- Output Voltage: 220vac

- Upper Bypass limit: 264vac

- Lower Bypass limit: 154vac

- Allowable Frequency range for UPS bypass: Auto sensing

- Power Quality Sensitivity: Automatic

--------------------------------------------------------

Can anyone see any issues or risks if going with this configuration?

Should I stick to the default configuration?

Any assistance will be much appreciated.

Kind regards,

Janko

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 6000xli
  • configuration
  • power
  • surt
  • voltage
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-12 12:53 AM

0 Likes
0
10477
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-12 12:53 AM

The way it looks to me, I don't think there is a need to change the factory settings... you will not really have anything to gain by it. The upper and lower bypass settings don't come into play in power outage situations where the UPS is deciding whether to go to battery, but rather they apply in cases where the UPS has an internal fault or is overloaded and needs to go to bypass - in that situation based on the current settings if the incoming voltage is above 253 it will drop the loads instead of going to bypass to avoid damaging the loads. Changing the upper bypass to a higher value is in fact risky, as I mentioned before because the UPS will pass an even higher voltage ( IE higher than 253 ) to the loads if it has a fault and goes to bypass. Your current output voltage setting of 230 should be ok as your networking and server hardware should be good on inputs of up to 240 volts. If you have the option of lowering the output voltage to 220 to match the input that would be ok too.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-12 12:53 AM

0 Likes
0
10477
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-12 12:53 AM

Hello, need some additional info before suggesting anything firm:

1. Are you having a problem with any transfers to battery caused by the input voltage swings ?   (... if not there isn't much reason to tweak the factory settings, really, as you aren't subjecting the UPS to unnecessary wear and tear and all your devices are in the protected range ).

2. Is the nominal UPS supply (Input) voltage supposed to be 230 volts ?   ( I see you are in Denmark so I am guessing the answer is yes... 230 V @ 50 Hz)

3. What is the input voltage range rating of the power supplies for your Cisco and HP hardware ?

....here in Canada our Cisco power supplies are usually able to accept  100 to 240 VAC range, for example, so if this is the same for your hardware I would not recommend changing your upper bypass setting any higher (eg to 264 volts) you risk blowing up the power supplies if  your UPS has a fault and goes into bypass.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-12 12:53 AM

0 Likes
0
10477
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-12 12:53 AM

Hello Battman, many thanks for your input.

Here is some additional info.

1. There are no problem with trasfers to batteries and yes, I would prefer not to tweak with factory setting.

2. I am located in Angola where the nominal input voltage here is 220V@50Hz.

The challenge in this respect is that the local power lines are not reliable. There are daily outages.

Thus I have been thinking if it make sense to tweak 'Lower & Upper Voltage Bypass' limits.

3. All IT equipment have been until now connected to one of SURT6000XLI that delivers output voltage 230V@50Hz.

Which one of the following configurations makes most sense and are there any risks associated?

Tweek the factory settings according to the nominal power line conditions in Angola:

--------------------------------------------------

- Nominal Input Voltage: 220vac

- UPS Output Voltage: 220vac

- Upper Bypass limit: 264vac

- Lower Bypass limit: 154vac

- Allowable Frequency range for UPS bypass: Auto sensing

- Power Quality Sensitivity: Automatic

--------------------------------------------------------

or keep the factory settings:

--------------------------------------------------------

- Nominal Input Voltage: 220vac

- UPS Output Voltage: 230vac

- Upper Bypass limit: 253vac

- Lower Bypass limit: 161vac

- Allowable Frequency range for UPS bypass: Auto sensing

- Power Quality Sensitivity: Automatic

--------------------------------------------------------

Thanks.

Regards,

Janko

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-12 12:53 AM

0 Likes
0
10478
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-12 12:53 AM

The way it looks to me, I don't think there is a need to change the factory settings... you will not really have anything to gain by it. The upper and lower bypass settings don't come into play in power outage situations where the UPS is deciding whether to go to battery, but rather they apply in cases where the UPS has an internal fault or is overloaded and needs to go to bypass - in that situation based on the current settings if the incoming voltage is above 253 it will drop the loads instead of going to bypass to avoid damaging the loads. Changing the upper bypass to a higher value is in fact risky, as I mentioned before because the UPS will pass an even higher voltage ( IE higher than 253 ) to the loads if it has a fault and goes to bypass. Your current output voltage setting of 230 should be ok as your networking and server hardware should be good on inputs of up to 240 volts. If you have the option of lowering the output voltage to 220 to match the input that would be ok too.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of