Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
UPS unable to send email notification during power events but test email works fine
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2511:51 PM. Last Modified: 2024-03-1903:08 AM
UPS unable to send email notification during power events but test email works fine
05/20/2020 13:07:56 Device UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon. 0x010F 05/20/2020 13:07:03 System Email: Could not resolve 'mail.intersil.com'. 0x001A 05/20/2020 13:06:14 System Email: Could not resolve 'mail.intersil.com'. 0x001A 05/20/2020 13:05:03 System Email: Could not resolve 'mail.intersil.com'. 0x001A 05/20/2020 13:04:14 System Email: Could not resolve 'mail.intersil.com'. 0x001A 05/20/2020 13:03:25 Device UPS: On battery power in response to low input voltage. 0x0109 05/20/2020 13:03:25 Device UPS: Bypass not in range ; distorted waveform. 0x020F 05/20/2020 12:25:10 System Email: Could not resolve 'mail.intersil.com'. 0x001A 05/20/2020 12:24:21 System Email: Could not resolve 'mail.intersil.com'. 0x001A 05/20/2020 12:23:32 System Email: Could not resolve 'mail.intersil.com'. 0x001A 05/20/2020 12:23:26 Device UPS: No longer on battery power. 0x010A 05/20/2020 12:23:25 Device UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 0x0210 05/20/2020 12:22:43 System Email: Could not resolve 'mail.intersil.com'. 0x001A 05/20/2020 12:21:54 Device UPS: Bypass not in range ; distorted waveform. 0x020F 05/20/2020 12:21:54 Device UPS: On battery power in response to distorted input. 0x0109
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2511:51 PM. Last Modified: 2024-03-1903:08 AM
Hi,
You should check to be sure the NMC is not losing Internet access during the power events. The error indicates the NMC is attempting to send the mail but cannot access the server.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2511:51 PM. Last Modified: 2024-03-1903:08 AM
Hi,
You should check to be sure the NMC is not losing Internet access during the power events. The error indicates the NMC is attempting to send the mail but cannot access the server.