UPS switching to battery and back to mains

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS switching to battery and back to mains
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:50 AM . Last Modified: ‎2024-03-12 11:08 PM

0 Likes
7
2114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:50 AM . Last Modified: ‎2024-03-12 11:08 PM

UPS switching to battery and back to mains

 

Hi,

 

About once a week our UPS switches to battery and immediately back to mains power.

 

Example from the log:

08/24/2013     02:09:42     UPS: A discharged battery condition no longer exists.

08/24/2013     02:09:41     UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.

 

We have reduced sensitivity to Low (UPS\Configuration\Power Settings\Sensitivity) but the issue persists.

 

We've had an electrician monitor the line for 4 days and the results came out within normal range.

 

Can anyone please advise why this is happening and how we can stop it?

 

https://s11.postimg.org/t817c2kpv/UPS.png

 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:50 AM . Last Modified: ‎2024-03-12 11:08 PM

0 Likes
0
2114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:50 AM . Last Modified: ‎2024-03-12 11:08 PM

You do have some on battery events between mid-end July and early August..

07/25/2013 20:22:57 UPS: No longer on battery power. 0x010A

07/25/2013 20:22:56 UPS: On battery power in response to distorted input. 0x0109

07/24/2013 07:05:35 UPS: No longer on battery power. 0x010A

07/24/2013 07:05:35 UPS: On battery power in response to distorted input. 0x0109

So the sensitivity might have helped with those and preventing battery transfers but it does not have anything to do with these types:

08/20/2013 14:40:19 UPS: A discharged battery condition no longer exists. 0x0108

08/20/2013 14:40:10 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately. 0x0107

Anyway, I believe the root cause is low reported runtime being within two minutes of your low battery duration which you've now lowered..

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:50 AM . Last Modified: ‎2024-03-12 11:08 PM

0 Likes
0
2115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:50 AM . Last Modified: ‎2024-03-12 11:08 PM

You do have some on battery events between mid-end July and early August..

07/25/2013 20:22:57 UPS: No longer on battery power. 0x010A

07/25/2013 20:22:56 UPS: On battery power in response to distorted input. 0x0109

07/24/2013 07:05:35 UPS: No longer on battery power. 0x010A

07/24/2013 07:05:35 UPS: On battery power in response to distorted input. 0x0109

So the sensitivity might have helped with those and preventing battery transfers but it does not have anything to do with these types:

08/20/2013 14:40:19 UPS: A discharged battery condition no longer exists. 0x0108

08/20/2013 14:40:10 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately. 0x0107

Anyway, I believe the root cause is low reported runtime being within two minutes of your low battery duration which you've now lowered..

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:50 AM . Last Modified: ‎2024-03-12 11:08 PM

0 Likes
0
2114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:50 AM . Last Modified: ‎2024-03-12 11:08 PM

Thanks Angela, glad we got this sorted.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:50 AM . Last Modified: ‎2024-03-12 11:08 PM

0 Likes
0
2114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:50 AM . Last Modified: ‎2024-03-12 11:08 PM

Can anyone please advise?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:50 AM . Last Modified: ‎2024-03-12 11:07 PM

0 Likes
0
2113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:50 AM . Last Modified: ‎2024-03-12 11:07 PM

Could you please attach the full logs from your Network Management Card, which you can get via FTP?

My thought is that the load is fluctuating and goes a little higher and what happens is your runtime is shrinking with the higher load, probably within 2 minutes of your low battery signaling time (the runtime remaining value that the UPS deems "low battery"), so it is trying to tell you that maybe your battery is "discharged" and doesn't have much runtime left if this is a power outage at that time. Your runtime is on the screen at about 7 minutes. The default low battery signaling time is 2 minutes so if its dropping down to 4, this could be the issue. The log files will help me verify all of this. I need event.txt, config.ini, and data.txt. Feel free to remove any IP addresses, etc before posting if you'd like.

Instructions on obtaining log files are here -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...

Lastly, what model UPS is this? How old is the battery in the UPS? How long does the UPS normally run on battery with your average load (7 minutes or so)?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:50 AM . Last Modified: ‎2024-03-12 11:07 PM

0 Likes
0
2113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:50 AM . Last Modified: ‎2024-03-12 11:07 PM

Thanks for your response Angela, please see logs attached to this post.

Regarding your thought about the high load, the issue with the unit switching to battery and immediately back to mains started from Day 1. The load then was 55%, it has since increased as per the image in the first post.

To answer your questions I've copied this from the About page (the unit was purchased and installed on 4/2013):

Model:     Smart-UPS X 1500

Serial Number:     AS1234125326

Firmware Revision:     UPS 09.1 / MCU 09.1 / UBL 06.9 / MBL 06.0 (ID20)

Manufacture Date:     08/23/2012

Apparent Power Rating:     1440 VA

Real Power Rating:     1200 W

When the load was 55%, I ran a  test and the battery lasted for around 17 minutes. I haven't performed a test since the load has increased.

Attachments
logs-obfuscated.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:50 AM . Last Modified: ‎2024-03-12 11:07 PM

0 Likes
0
2113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:50 AM . Last Modified: ‎2024-03-12 11:07 PM

To clarify, the events from your first post DO NOT indicate the UPS switching back and forth from battery. They indicate your runtime is low and typically that happens when it has been discharged. It can also happen in your situation with no battery events and a charged battery but just plain ol low runtime. The batteries are probably around a year old, just as the UPS is. If there are not frequent battery transfers or a calibration was not done to recalculate available runtime, we may need to do that.

Also, I am missing event.txt and need that place. I did not need dump.txt and debug.txt.

Lastly, your low battery duration in the config.ini has been raised from two minutes to five (LowBatteryDuration=5 per config.ini). This means when your reported runtime comes within two minutes (or below) 7, you'll see this alarms but again, it does not indicate any battery operation.


I'll need event.txt to verify nothing else is going on or that there are not other events you're seeing to indicate battery operation because so far, I see nothing to indicate it has been transferring. So, it makes sense that changing sensitivity did not do anything.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:51 AM . Last Modified: ‎2024-03-12 11:07 PM

0 Likes
0
2113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:51 AM . Last Modified: ‎2024-03-12 11:07 PM

 

Hi,

 

About once a week our UPS switches to battery and immediately back to mains power.

 

Example from the log:

08/24/2013     02:09:42     UPS: A discharged battery condition no longer exists.

08/24/2013     02:09:41     UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.

 

We have reduced sensitivity to Low (UPS\Configuration\Power Settings\Sensitivity) but the issue persists.

 

We've had an electrician monitor the line for 4 days and the results came out within normal range.

 

Can anyone please advise why this is happening and how we can stop it?

 

https://s11.postimg.org/t817c2kpv/UPS.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore