Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-28 11:42 PM . Last Modified: 2024-03-14 01:22 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:42 PM . Last Modified: 2024-03-14 01:22 AM
I have a customer that has told me that at least 2 of his UPS's that were on battery due to power outage, ran down the battery and shut off. Now, when they do shut off, aren't they suppose to come back on when the batteries charge to a certain percentage? Is there something they have to do with the powerchute software? That's what I am assuming. Any help will be greatly appreciated. Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:42 PM . Last Modified: 2024-03-14 01:22 AM
hi martin, it should work as described. there could be a few other issues with configuration though.
can you post the config.ini (remove any personal data if you want), data.txt and event.txt here so we can review? also please note any applicable times in the logs we can look at for behavior you described.
here are instructions on downloading log files: http://nam-en.apc.com/app/answers/detail/a_id/9321
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:42 PM . Last Modified: 2024-03-14 01:22 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:42 PM . Last Modified: 2024-03-14 01:22 AM
I have a customer that has told me that at least 2 of his UPS's that were on battery due to power outage, ran down the battery and shut off. Now, when they do shut off, aren't they suppose to come back on when the batteries charge to a certain percentage? Is there something they have to do with the powerchute software? That's what I am assuming. Any help will be greatly appreciated. Thanks!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:42 PM . Last Modified: 2024-03-14 01:22 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:42 PM . Last Modified: 2024-03-14 01:22 AM
I know this is an old thread, but I have the exact same issue. I run a smart 6000 RT with the network management card, and we had some issues with power failures, I configured the minimum battery capacity to 50% and the time delay to 120. I assumed this would turn back on 120 secs. after the 50% was reached. However the UPS needed manual intervention which is not what I was looking for. Does a combination of both negate each other? Any help would be greatly appreciated.
Martin
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:42 PM . Last Modified: 2024-03-14 01:22 AM
hi martin, it should work as described. there could be a few other issues with configuration though.
can you post the config.ini (remove any personal data if you want), data.txt and event.txt here so we can review? also please note any applicable times in the logs we can look at for behavior you described.
here are instructions on downloading log files: http://nam-en.apc.com/app/answers/detail/a_id/9321
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.