Posted: 2021-06-28 11:42 PM . Last Modified: 2024-03-14 01:22 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:42 PM . Last Modified: 2024-03-14 01:22 AM
I have 6 UPS's with AP9617 management cards installed and configured. When you bring up the URL to each card it allows me to shut down and restart the UPS's. Is there a card, software or APC solution that allows me to shut down specific ports and restart them instead of the entire UPS?
Just trying to save a drive into the data center when I can't get into the server remotely. Would like to just restart the UPS power ports of that server that is affected.
Tried doing a search and look on the products page. Hoping I can buy another management card or something that isn't going to be really expensive.
Thx for any help or input.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:42 PM . Last Modified: 2024-03-14 01:22 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:42 PM . Last Modified: 2024-03-14 01:22 AM
I have 6 UPS's with AP9617 management cards installed and configured. When you bring up the URL to each card it allows me to shut down and restart the UPS's. Is there a card, software or APC solution that allows me to shut down specific ports and restart them instead of the entire UPS?
Just trying to save a drive into the data center when I can't get into the server remotely. Would like to just restart the UPS power ports of that server that is affected.
Tried doing a search and look on the products page. Hoping I can buy another management card or something that isn't going to be really expensive.
Thx for any help or input.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:42 PM . Last Modified: 2024-03-14 01:22 AM
You can buy a [switched rack PDU|http://www.apc.com/products/family/index.cfm?id=70], which has controllable outlets. Some (though not many) UPSes also have the option of controllable outlet groups, like the [SUM1500RMXL2U|http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SUM1500RMXL2U]. The management cards cannot control individual outlets in the UPS, though.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:42 PM . Last Modified: 2024-03-14 01:22 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:42 PM . Last Modified: 2024-03-14 01:22 AM
I have 6 UPS's with AP9617 management cards installed and configured. When you bring up the URL to each card it allows me to shut down and restart the UPS's. Is there a card, software or APC solution that allows me to shut down specific ports and restart them instead of the entire UPS?
Just trying to save a drive into the data center when I can't get into the server remotely. Would like to just restart the UPS power ports of that server that is affected.
Tried doing a search and look on the products page. Hoping I can buy another management card or something that isn't going to be really expensive.
Thx for any help or input.