UPS is not powering off, after shutdown event

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS is not powering off, after shutdown event
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-09 01:43 AM . Last Modified: ‎2024-02-14 11:28 PM

0 Likes
8
984
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 01:43 AM . Last Modified: ‎2024-02-14 11:28 PM

UPS is not powering off, after shutdown event

Dear All,

I have the next problem.

I have a licensed vmware ESXI 6.5. There i have installed virtual appliance PCNS.

Startup/Shutdown VM's is configured on esxi host

My Ups is : APC Smart Ups 2200(SMT2200RMI2U)

My NMC is -AP9630

I configured PCNS to power off snadalone esxi host.

I'll post screenshots below.

When the power is absent ups is working till it reach "Low battery duration"(it's 30 minutes in my case).

Than UPS send and information to PCNS, and it send a command to esxi to shutdown the host.

Than host shuts down, and VM's also are shutting down correctly, and that the host is also shuted down.

But the main problem is that UPS is not powering off after the host is down.  After the server is down the UPS Runtime Remaining changing to 1 hour. So if the power will be restored for this 1 hour, my server will not be switched on.

Please help me to fix it.

See the screenshots please:

J5jbpAo8CAGHR77ol8RToQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpegJ5jbpAo8CAGHR77ol8RToQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg

Echzgq7yzrLW0dntQxWEGg%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpegEchzgq7yzrLW0dntQxWEGg%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg

8HG9tKPuKKSvnpH6KnonIQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg8HG9tKPuKKSvnpH6KnonIQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg

And please see the PCNS screenshotsVQ2GSmz3iIAkvTHiIcBDmQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpegVQ2GSmz3iIAkvTHiIcBDmQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg

%2BkIg9XfYbuwiNnxoHgXVaw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg%2BkIg9XfYbuwiNnxoHgXVaw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg

If i need to post some additional screenshots please let me know.

Best regards

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 01:43 AM . Last Modified: ‎2024-02-14 11:28 PM

0 Likes
0
984
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 01:43 AM . Last Modified: ‎2024-02-14 11:28 PM

Hi,

Not sure why the NMC is ignoring or not receiving the power down command but there is a work around. Assuming the ESXi host is plugged into the Main outlet group (Group 0) you can go to Outlet Group Settings for Main, select Load Shedding, Runtime remaining is less than and enter 1800 seconds, deselect Skip outlet off delay, set the Outlet off delay to the needed time ot power down the VMs and host, and select Apply. Example 2 minutes to power down VMs, 4 minutes to power down ESXi host, 2 minutes for VMs to restart, so set power down delay to 8 minutes. Also, changed the low battery duration to 20 minute to avoid any conflict. 

When the UPS runtime remaining falls below 30 minutes the PowerChute client will be informed and the shutdown process will start. The outlet group will remain powered for 8 minutes (you may want to add an extra 2 minutes for safety) and then AC will be cut to all outlet groups. The NMC will remain powered up for an additional 9 minutes and then go off line. When AC is restored assuming you do not deselect Restart when power is restored or select Stay off after power return when AC is restored the outlet groups will be energized. 

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 01:43 AM . Last Modified: ‎2024-02-14 11:28 PM

0 Likes
0
984
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 01:43 AM . Last Modified: ‎2024-02-14 11:28 PM

Hi,

Please provide the NMC config.ini file and the NMC event log. If the NMC is running firmware version 6.0 or above you can access the log by going to About - Support and select Generate Logs. Download them and attach to the post. 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-09 01:43 AM . Last Modified: ‎2024-02-14 11:28 PM

0 Likes
0
984
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 01:43 AM . Last Modified: ‎2024-02-14 11:28 PM

Please find the required files:

Attachments
APC.7z
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 01:43 AM . Last Modified: ‎2024-02-14 11:28 PM

0 Likes
0
984
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 01:43 AM . Last Modified: ‎2024-02-14 11:28 PM

Hi,

The event log does not show that the NMC registered the power off command from PCNS. Up-grade the firmware on the NMC should resolve the issue. The lastest firmware can be downloaded from http://www.apc.com/us/en/tools/download/

Select Firmware Upgrades - UPS Network Management Card  The select SFSUMX650

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-09 01:43 AM . Last Modified: ‎2024-02-14 11:28 PM

0 Likes
0
984
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 01:43 AM . Last Modified: ‎2024-02-14 11:28 PM

Dear Bill,

Thank you for our reply.

I've upgraded firmware, but i'll have a possibility to test it on next week. I'll come back with result.

Best regards

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-09 01:43 AM . Last Modified: ‎2024-02-14 11:28 PM

0 Likes
0
984
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 01:43 AM . Last Modified: ‎2024-02-14 11:28 PM

Dear Bill,

After the firmware upgrade the situation is the same.

Please find new logs in att.

Attachments
Logs.7z
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 01:43 AM . Last Modified: ‎2024-02-14 11:28 PM

0 Likes
0
984
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 01:43 AM . Last Modified: ‎2024-02-14 11:28 PM

Hi,

Sorry for the inconvenience. Did PowerChute record sending the shutdown signal to the NMC because the NMC is still not recording receiving the signal. 

Question do you want all outlet groups to power down at the same time or staggered? As it stands now with your configuration they all should go off at the same time. 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-09 01:43 AM . Last Modified: ‎2024-02-14 11:28 PM

0 Likes
0
984
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 01:43 AM . Last Modified: ‎2024-02-14 11:28 PM

It's not important for me.

I have just one cable connected to UPS.

I just need the whole UPS to power down, after the Vmware Host is shutted down.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 01:43 AM . Last Modified: ‎2024-02-14 11:28 PM

0 Likes
0
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 01:43 AM . Last Modified: ‎2024-02-14 11:28 PM

Hi,

Not sure why the NMC is ignoring or not receiving the power down command but there is a work around. Assuming the ESXi host is plugged into the Main outlet group (Group 0) you can go to Outlet Group Settings for Main, select Load Shedding, Runtime remaining is less than and enter 1800 seconds, deselect Skip outlet off delay, set the Outlet off delay to the needed time ot power down the VMs and host, and select Apply. Example 2 minutes to power down VMs, 4 minutes to power down ESXi host, 2 minutes for VMs to restart, so set power down delay to 8 minutes. Also, changed the low battery duration to 20 minute to avoid any conflict. 

When the UPS runtime remaining falls below 30 minutes the PowerChute client will be informed and the shutdown process will start. The outlet group will remain powered for 8 minutes (you may want to add an extra 2 minutes for safety) and then AC will be cut to all outlet groups. The NMC will remain powered up for an additional 9 minutes and then go off line. When AC is restored assuming you do not deselect Restart when power is restored or select Stay off after power return when AC is restored the outlet groups will be energized. 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of