We Value Your Feedback! Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services. Learn more about the survey or Click here to Launch the survey Schneider Electric Services Innovation Team!
UPS WITH ALARMS OF RECTIFIER NOT WORKING, INCORRECT DC VOLTAGE AND INACTIVE PFC
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-1308:14 AM
UPS WITH ALARMS OF RECTIFIER NOT WORKING, INCORRECT DC VOLTAGE AND INACTIVE PFC
Hello Schneider team and community,
We are operating a Schneider Easy UPS 3M, 160 kVA / 160 kW, installed in a hospital environment powering critical loads. The UPS is intermittently displaying the following alarms simultaneously:
E:05 – Rectifier not working
E:10 – DC Bus voltage incorrect
PFC inactive
When these alarms appear, the unit automatically transfers to bypass. After a few seconds, it recovers on its own and switches back to normal double-conversion operation.
🔧Current firmware version: 3.2.1.1 📦Model: Easy UPS 3M 160 kVA (Advanced version with hot-swappable power modules) 📍Location: Hospital – critical loads
A Schneider Electric expert advised the following:
“This UPS contains a power module in which the charger, PFC, and rectifier components are integrated into a single board. When the system detects incorrect DC bus voltage along with a rectifier fault and PFC inactive status, it points to a likely failure within that module. According to our field documentation, the recommended solution is to replace the full power module.”
They also recommended updating the UPS firmware as part of the corrective action.