UPS: The output power is turned off.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS: The output power is turned off.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:37 AM . Last Modified: ‎2024-03-17 11:56 PM

0 Likes
0
962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:37 AM . Last Modified: ‎2024-03-17 11:56 PM

UPS: The output power is turned off.

I have a Smart-UPS X 3000 that has been in production for 4 months now and I am having a few issues with it. I had it unexpectedly shutdown last night and I have no clue as to why it would have. Its an old building where we have the UPS and I know they have brownouts at times but the UPS is only on battery for a few seconds to a minute at a time which isn't long enough for the batteries to die.

Here is the log file:

Network Management Card AOS v6.4.0
Smart-UPS & Matrix-UPS APP v6.4.0
NMC Serial Number: 5A1721T35654
Date Time Name Contact Location System IP
08/01/2018 08:58:40 apcDD7855 Unknown Unknown 192.168.61.18
Date Time User Event Code
08/01/2018 08:58:28 b Web user 'b' logged in from 2.2.2.2. 0x0015
08/01/2018 08:55:23 System Web user 'b' logged out from 2.2.2.2. 0x001F
08/01/2018 08:54:42 b SSH CLI user 'b' logged in from 2.2.2.2. 0x0014
08/01/2018 08:43:38 b Web user 'b' logged in from 2.2.2.2. 0x0015
07/31/2018 18:19:26 System Email: Could not mail '1.1.1.1'. 0x001A
07/31/2018 18:18:53 System Email: Could not mail '1.1.1.1'. 0x001A
07/31/2018 18:18:21 Device UPS: No longer on battery power. 0x010A
07/31/2018 18:18:19 Device UPS: On battery power in response to distorted input. 0x0109
07/31/2018 17:12:01 Device UPS: Self-Test passed. 0x0105
07/31/2018 17:11:53 Device UPS: Self-Test started by automatic timer. 0x0137
07/31/2018 17:11:36 Device UPS: The output power is now turned on. 0x0113
07/31/2018 17:11:36 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
07/31/2018 17:11:36 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
07/31/2018 17:11:36 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
07/31/2018 17:11:36 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to turn on, sequenced. 0x0174
07/31/2018 17:11:36 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to turn on, sequenced. 0x0174
07/31/2018 17:11:36 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to turn on, sequenced. 0x0174
07/31/2018 17:11:31 System Email: Could not mail '1.1.1.1'. 0x001A
07/31/2018 17:10:58 Device UPS: The output power is turned off. 0x0114
07/31/2018 17:10:58 Device UPS: The graceful shutdown period has ended. 0x014F
07/31/2018 17:10:57 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
07/31/2018 17:10:57 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
07/31/2018 17:10:57 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
07/28/2018 00:20:43 Device UPS: Self-Test passed. 0x0105
07/28/2018 00:20:36 Device UPS: Self-Test started by automatic timer. 0x0137
07/25/2018 13:14:31 System NTP update successful. 0x004A
07/20/2018 21:22:26 Device UPS: Self-Test passed. 0x0105
07/20/2018 21:22:18 Device UPS: Self-Test started by automatic timer. 0x0137
07/13/2018 21:03:05 Device UPS: No longer compensating for a low input voltage. 0x010C
07/13/2018 21:03:05 Device UPS: Compensating for a low input voltage. 0x010B
07/13/2018 18:24:27 Device UPS: Self-Test passed. 0x0105
07/13/2018 18:24:19 Device UPS: Self-Test started by automatic timer. 0x0137
07/11/2018 13:13:59 System NTP update successful. 0x004A
07/06/2018 15:26:10 Device UPS: Self-Test passed. 0x0105
07/06/2018 15:26:02 Device UPS: Self-Test started by automatic timer. 0x0137
07/04/2018 21:30:47 Device UPS: No longer on battery power. 0x010A
07/04/2018 21:30:46 Device UPS: On battery power in response to rapid change of input. 0x0109
07/04/2018 19:36:18 Device UPS: No longer on battery power. 0x010A
07/04/2018 19:36:17 Device UPS: On battery power in response to rapid change of input. 0x0109
07/04/2018 19:35:44 Device UPS: No longer on battery power. 0x010A
07/04/2018 19:35:43 Device UPS: On battery power in response to rapid change of input. 0x0109
07/04/2018 19:35:35 Device UPS: No longer on battery power. 0x010A
07/04/2018 19:35:34 Device UPS: On battery power in response to distorted input. 0x0109
07/04/2018 19:33:37 Device UPS: No longer on battery power. 0x010A
07/04/2018 19:33:36 Device UPS: On battery power in response to distorted input. 0x0109
07/04/2018 19:33:25 Device UPS: No longer on battery power. 0x010A
07/04/2018 19:33:24 Device UPS: On battery power in response to distorted input. 0x0109
07/04/2018 19:33:05 Device UPS: No longer on battery power. 0x010A
07/04/2018 19:33:04 Device UPS: On battery power in response to distorted input. 0x0109
07/03/2018 06:03:00 Device UPS: No longer on battery power. 0x010A
07/03/2018 06:02:59 Device UPS: On battery power in response to distorted input. 0x0109
06/29/2018 12:28:11 Device UPS: Self-Test passed. 0x0105
06/29/2018 12:28:02 Device UPS: Self-Test started by automatic timer. 0x0137
06/27/2018 13:13:28 System NTP update successful. 0x004A
06/22/2018 09:29:54 Device UPS: Self-Test passed. 0x0105
06/22/2018 09:29:46 Device UPS: Self-Test started by automatic timer. 0x0137
06/18/2018 15:00:28 Device UPS: No longer on battery power. 0x010A
06/18/2018 15:00:27 Device UPS: On battery power in response to distorted input. 0x0109
06/18/2018 15:00:22 Device UPS: No longer compensating for a low input voltage. 0x010C
06/18/2018 15:00:22 Device UPS: Compensating for a low input voltage. 0x010B
06/18/2018 14:54:15 Device UPS: No longer on battery power. 0x010A
06/18/2018 14:54:14 Device UPS: On battery power in response to distorted input. 0x0109
06/16/2018 02:49:30 Device UPS: No longer on battery power. 0x010A
06/16/2018 02:49:29 Device UPS: On battery power in response to distorted input. 0x0109
06/16/2018 01:13:12 Device UPS: No longer on battery power. 0x010A
06/16/2018 01:13:11 Device UPS: On battery power in response to distorted input. 0x0109
06/15/2018 06:31:55 Device UPS: Self-Test passed. 0x0105
06/15/2018 06:31:46 Device UPS: Self-Test started by automatic timer. 0x0137
06/13/2018 13:12:56 System NTP update successful. 0x004A
06/10/2018 06:43:57 Device UPS: No longer on battery power. 0x010A
06/10/2018 06:43:55 Device UPS: On battery power in response to distorted input. 0x0109
06/08/2018 03:33:37 Device UPS: Self-Test passed. 0x0105
06/08/2018 03:33:29 Device UPS: Self-Test started by automatic timer. 0x0137
06/01/2018 09:49:01 System Email: Could not mail '1.1.1.1'. 0x001A
06/01/2018 09:48:27 System Email: Could not mail '1.1.1.1'. 0x001A
06/01/2018 09:47:53 System Email: Could not mail '1.1.1.1'. 0x001A
06/01/2018 09:47:19 System Email: Could not mail '1.1.1.1'. 0x001A
06/01/2018 09:46:45 System Email: Could not mail '1.1.1.1'. 0x001A
06/01/2018 09:45:56 Device UPS: Restored the local network management interface-to-UPS communication. 0x0101
06/01/2018 09:45:43 System Network service started. IPv6 address FE80::2C0:B7FF:FEDD:7855 assigned by link-local autoconfiguration. 0x0007
06/01/2018 09:45:41 System Network service started. System IP is 192.168.61.18 from manually configured settings. 0x0007
06/01/2018 09:45:32 System Network Interface restarted. 0x0002
06/01/2018 00:35:38 Device UPS: Self-Test passed. 0x0105
06/01/2018 00:35:30 Device UPS: Self-Test started by automatic timer. 0x0137
05/30/2018 13:12:12 System NTP update successful. 0x004A
05/24/2018 21:37:23 Device UPS: Self-Test passed. 0x0105
05/24/2018 21:37:15 Device UPS: Self-Test started by automatic timer. 0x0137
05/18/2018 11:07:17 System Email: Could not mail '1.1.1.1'. 0x001A
05/18/2018 11:06:43 System Email: Could not mail '1.1.1.1'. 0x001A
05/18/2018 11:06:09 System Email: Could not mail '1.1.1.1'. 0x001A
05/18/2018 11:05:35 System Email: Could not mail '1.1.1.1'. 0x001A
05/18/2018 11:05:01 System Email: Could not mail '1.1.1.1'. 0x001A
05/18/2018 11:04:12 Device UPS: Restored the local network management interface-to-UPS communication. 0x0101
05/18/2018 11:03:58 System Network service started. IPv6 address FE80::2C0:B7FF:FEDD:7855 assigned by link-local autoconfiguration. 0x0007
05/18/2018 11:03:56 System Network service started. System IP is 192.168.61.18 from manually configured settings. 0x0007
05/18/2018 11:03:48 System Network Interface restarted. 0x0002
05/17/2018 18:39:23 Device UPS: Self-Test passed. 0x0105
05/17/2018 18:39:14 Device UPS: Self-Test started by automatic timer. 0x0137
05/17/2018 05:07:32 Device UPS: No longer on battery power. 0x010A
05/17/2018 05:07:31 Device UPS: On battery power in response to distorted input. 0x0109
05/17/2018 05:07:26 Device UPS: No longer on battery power. 0x010A
05/17/2018 05:07:26 Device UPS: No longer compensating for a low input voltage. 0x010C
05/17/2018 05:07:25 Device UPS: On battery power in response to distorted input. 0x0109
05/17/2018 05:07:25 Device UPS: Compensating for a low input voltage. 0x010B
05/16/2018 13:11:29 System NTP update successful. 0x004A
05/12/2018 21:50:39 Device UPS: No longer on battery power. 0x010A
05/12/2018 21:50:38 Device UPS: On battery power in response to distorted input. 0x0109
05/10/2018 15:41:07 Device UPS: Self-Test passed. 0x0105
05/10/2018 15:40:59 Device UPS: Self-Test started by automatic timer. 0x0137
05/03/2018 12:43:07 Device UPS: Self-Test passed. 0x0105
05/03/2018 12:42:59 Device UPS: Self-Test started by automatic timer. 0x0137
05/02/2018 13:10:58 System NTP update successful. 0x004A
04/26/2018 09:44:53 Device UPS: Self-Test passed. 0x0105
04/26/2018 09:44:46 Device UPS: Self-Test started by automatic timer. 0x0137
04/19/2018 06:46:52 Device UPS: Self-Test passed. 0x0105
04/19/2018 06:46:44 Device UPS: Self-Test started by automatic timer. 0x0137
04/18/2018 13:10:27 System NTP update successful. 0x004A
04/13/2018 21:19:06 Device UPS: No longer on battery power. 0x010A
04/13/2018 21:19:05 Device UPS: On battery power in response to distorted input. 0x0109
04/12/2018 03:48:40 Device UPS: Self-Test passed. 0x0105
04/12/2018 03:48:31 Device UPS: Self-Test started by automatic timer. 0x0137

UPS Status
Smart-UPS X 3000
Last Battery Transfer
Detection of distorted input
Battery Temperature
28.6°C
Runtime Remaining
3hr 34min 19sec
UPS Input
Input Voltage
117.9  VAC @  60.0  Hz
UPS Output
Output Voltage
117.9  VAC @  60.0  Hz
Load Current
1.2  Amps
Output VA
4.8 %
Output Watts
4.4 %
Output Efficiency
load too low
Output Energy Usage
420.46 kWh
Battery Status
State of Charge
100.0 %
Battery Voltage
135.6  VDC
Num of External Batteries
0
Next Battery Replacement Date
07/05/2022
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore