UPS Password

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS Password
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:09 AM

0 Likes
1
1924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:09 AM

UPS Password

I have a 5000VA UPS on a remote site, I think the network card is an AP9619. I am unable to access this UPS with the username and password I have?.

Is there someway of breaking into the UPS remotely?. I need to check the battery life and we don't have any technical staff on that site?.

Thanks

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:09 AM

0 Likes
0
1924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:09 AM

The only way to access an AP9619 once the password has been lost is locally. These cards do not have a "backdoor" like some of our older network-enabled products. You can follow the procedure outlined in our public knowledge-base # 7879:

1. Select a Serial port as a local computer and disable any service that uses the port

2. Use the configuration cable shipped with the unit to connect the serial port on the computer to the serial port on the unit.
Please note the configuration cable varies depending on different APC devices:
For the Network Management Card installed to smartslot of an APC UPS, configuration cable is 940-0024;
For the rPDU, configuration cable is 940-0144;
For the EMU2 AP9319, EMU3 AP9340 and EMS AP9320, the configuration cable is 940-0103;

3. Run a terminal emulation program (such as HyperTerminal) and configure the selected port for 9600 bps with cable 940-0103 or 940-0144, 2400 bps with cable 940-0024 , 8 data bits, no parity, 1 stop bit and no flow control, and save the changes.


4. Press ENTER to display the Username prompt.


5. Press the Reset button on the management card, which will be located near the network jack.* The button is very small so it is likely you will need a paperclip


6. Wait (usually a few seconds) for the status light on the network jack to flash rapidly between green and amber and press the reset button again.


7. Press ENTER as many times as necessary to redisplay the Username prompt, then use "apc" for the username and password (if you take longer than 30 seconds to log on after the Username prompt is displayed, you must start the login procedure again at step 4.


8. From the Control Console menu select System and then User Manager.


9. Select Administrator, and change the Username and Password settings, both of which are now defined as apc


10. Press CTRL-C and log off

* Pressing the reset button on the network card will have no effect on the unit's operation.

Note: For network cards running less than version 2.5, step 6 (the second reset press) will not be necessary.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:09 AM

0 Likes
0
1925
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:09 AM

The only way to access an AP9619 once the password has been lost is locally. These cards do not have a "backdoor" like some of our older network-enabled products. You can follow the procedure outlined in our public knowledge-base # 7879:

1. Select a Serial port as a local computer and disable any service that uses the port

2. Use the configuration cable shipped with the unit to connect the serial port on the computer to the serial port on the unit.
Please note the configuration cable varies depending on different APC devices:
For the Network Management Card installed to smartslot of an APC UPS, configuration cable is 940-0024;
For the rPDU, configuration cable is 940-0144;
For the EMU2 AP9319, EMU3 AP9340 and EMS AP9320, the configuration cable is 940-0103;

3. Run a terminal emulation program (such as HyperTerminal) and configure the selected port for 9600 bps with cable 940-0103 or 940-0144, 2400 bps with cable 940-0024 , 8 data bits, no parity, 1 stop bit and no flow control, and save the changes.


4. Press ENTER to display the Username prompt.


5. Press the Reset button on the management card, which will be located near the network jack.* The button is very small so it is likely you will need a paperclip


6. Wait (usually a few seconds) for the status light on the network jack to flash rapidly between green and amber and press the reset button again.


7. Press ENTER as many times as necessary to redisplay the Username prompt, then use "apc" for the username and password (if you take longer than 30 seconds to log on after the Username prompt is displayed, you must start the login procedure again at step 4.


8. From the Control Console menu select System and then User Manager.


9. Select Administrator, and change the Username and Password settings, both of which are now defined as apc


10. Press CTRL-C and log off

* Pressing the reset button on the network card will have no effect on the unit's operation.

Note: For network cards running less than version 2.5, step 6 (the second reset press) will not be necessary.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore