How to properly configure servers and storage array shutdown during power loss for SRT8KRMXLI

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How to properly configure servers and storage array shutdown during power loss for SRT8KRMXLI
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:09 AM

0 Likes
3
1112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:09 AM

How to properly configure servers and storage array shutdown during power loss for SRT8KRMXLI

Hello!
As far as I understand, to turn off the servers I need to install and configure PS Network Shutdown on each of the servers. But there is no way to turn off the power of storage arrays. On the other hand, PS Business Edition  can turn off outlets with a load for any event. Therefore, I installed PS Business Edition on one server connected to a USB cable to UPS. However, I ran into some problems. I suspect that the problems are caused by the simultaneous connection to the network management card by the network, and by USB. If such a configuration is not functional, can I install an second control board in an empty slot? Is this the right way?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:08 AM

0 Likes
0
1112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:08 AM

Hi,

I have a few more questions.

  1. What is the available UPS runtime when all servers and the array are power on?
  2. Does the storage array need to be powered off cleanly or can it be turned off by pressing the power button?
  3. If it needs to be powered off cleanly can it be power off prior to all servers powering down or after all server have powered down?
  4. Will the storage array accept SSH command? 
  5. Does it have a built in shutdown app that will listen to USB?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:08 AM

0 Likes
0
1112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:08 AM

Hi,

I suggest you only use PowerChute Network Shutdown. 

  1. How many servers are plugged into the UPS?
  2. What outlet group is each server plugged into? 
  3. What outlet group is the storage array plugged into.
  4. What version of PowerChute Network Shutdown are you installing?
  5. What model network card is installed in the SRT?
  6. What version firmware is installed on the network card?
  7. When the UPS switches to battery do you want the shutdown started after the UPS runs on battery for x minutes or do you want the shutdown to start when the runtime remaining is x minutes?
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:08 AM

0 Likes
0
1112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:08 AM

1. six
2. group one and three
3. group two
4. 4.3.0 64-bit Windows
5. AP9537SUM (imbeded)
6. There was version 6.2. I upgraded to 6.8. It got worse.
7. I am ready to consider any option.

 

 

 

 

 

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:08 AM

0 Likes
0
1113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:08 AM

Hi,

I have a few more questions.

  1. What is the available UPS runtime when all servers and the array are power on?
  2. Does the storage array need to be powered off cleanly or can it be turned off by pressing the power button?
  3. If it needs to be powered off cleanly can it be power off prior to all servers powering down or after all server have powered down?
  4. Will the storage array accept SSH command? 
  5. Does it have a built in shutdown app that will listen to USB?
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore