PCNS and NMC2 settings for shutdown VM vCenter

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS and NMC2 settings for shutdown VM vCenter
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 04:45 AM . Last Modified: ‎2024-03-08 04:09 AM

0 Likes
3
2428
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:45 AM . Last Modified: ‎2024-03-08 04:09 AM

PCNS and NMC2 settings for shutdown VM vCenter

Good evening
I wanted to request information about the settings to be applied on an NMC2 and on the PCNS appliance to shutdown the VMs in the VMware environment when the battery runtime is approximately 20 minutes. I did not understand if the value assigned on PCNS prevails on NMC or vice versa

I am attaching the screenshot of the settings set on pcns and nmc

pcns

xdy%2Btk%2BD3HbsS6rBJJAqtA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngxdy%2Btk%2BD3HbsS6rBJJAqtA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

vSygAtMUTXvqx8AzdOXa2Q%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngvSygAtMUTXvqx8AzdOXa2Q%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

and nmc

o27upVELAYN5xTd3sqdGew%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngo27upVELAYN5xTd3sqdGew%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

 

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:45 AM . Last Modified: ‎2024-03-08 04:09 AM

0 Likes
0
2428
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:45 AM . Last Modified: ‎2024-03-08 04:09 AM

Hi,

They both will cause PowerChute to start the shutdown process when the runtime falls below 20 minutes. The low battery duration is used to trigger the shutdown process if no other event has been configured.

When the shutdown process begins the UPS will wait 20 minutes, plus a none configurable 2 minutes, plus the 90 second shutdown delay and then kill output to the outlets. As the graph below shows PowerChute will wait until the UPS reaches 20 minutes of runtime (the on battery event) then begin the process. 

akfKpCiM2gxXTYYMR%2FmO7A%3D%3D.pngakfKpCiM2gxXTYYMR%2FmO7A%3D%3D.png

If your system requires 20 minutes to power down I recommend increasing the runtime remaining threshold to start the shutdown process earlier. This will allow the system to power off and not drain the UPS batteries completely. I also recommend adding a start up delay to allow the batteries to charge in case of a second outage once the UPS turns back on. 

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:45 AM . Last Modified: ‎2024-03-08 04:09 AM

0 Likes
0
2429
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:45 AM . Last Modified: ‎2024-03-08 04:09 AM

Hi,

They both will cause PowerChute to start the shutdown process when the runtime falls below 20 minutes. The low battery duration is used to trigger the shutdown process if no other event has been configured.

When the shutdown process begins the UPS will wait 20 minutes, plus a none configurable 2 minutes, plus the 90 second shutdown delay and then kill output to the outlets. As the graph below shows PowerChute will wait until the UPS reaches 20 minutes of runtime (the on battery event) then begin the process. 

akfKpCiM2gxXTYYMR%2FmO7A%3D%3D.pngakfKpCiM2gxXTYYMR%2FmO7A%3D%3D.png

If your system requires 20 minutes to power down I recommend increasing the runtime remaining threshold to start the shutdown process earlier. This will allow the system to power off and not drain the UPS batteries completely. I also recommend adding a start up delay to allow the batteries to charge in case of a second outage once the UPS turns back on. 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:45 AM . Last Modified: ‎2024-03-08 04:09 AM

0 Likes
0
2428
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:45 AM . Last Modified: ‎2024-03-08 04:09 AM

Thanks a lot Bill.

For you, with a Smart-UPS 1500 which could be a start up delay and and in what field should I enter this data ?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:09 AM

0 Likes
0
2428
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:46 AM . Last Modified: ‎2024-03-08 04:09 AM

Another thing Bill

I can maximum put 23 minutes in nmc settings

Rc04Eq6bspxxayeqkyqQkg%3D%3D.pngRc04Eq6bspxxayeqkyqQkg%3D%3D.png

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore