I have around 225 Smart UPS's under my management, 1500's and 3000's. All have AP9630 network management card 2's installed.
Across the board, when the referenced event happens, it shows up in the ups event log, but does not send out a e-mail/trap notification. Nowhere in the event notification window is this alarm listed. Anyone know what theNMC event code is for this event? Was planning on solving my problem by dropping the event code into this and modifying appropriately--
http://10.1.1.1/eventdtl.htm?code=0x****
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:14 AM . Last Modified: 2024-03-18 02:36 AM
code=0x0109
"UPS: On battery power in response to an input power problem.[0x0109]"
With 225 UPSes, you might want to edit one of them, grab the .ini file from FTP, edit to leave only that particular event and the section header, then push to the other 224 UPSes or use the mass configuration tool to do this.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:14 AM . Last Modified: 2024-03-18 02:36 AM
code=0x0109
"UPS: On battery power in response to an input power problem.[0x0109]"
With 225 UPSes, you might want to edit one of them, grab the .ini file from FTP, edit to leave only that particular event and the section header, then push to the other 224 UPSes or use the mass configuration tool to do this.