UPS Network Management card 2 SMTP failure with O365

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS Network Management card 2 SMTP failure with O365
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
139
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:58 AM . Last Modified: ‎2024-03-11 12:18 AM

0 Likes
3
6755
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:58 AM . Last Modified: ‎2024-03-11 12:18 AM

UPS Network Management card 2 SMTP failure with O365

Hello,

I have a UPS Network Management Card 2 and i'm trying to setup SMTP notifications with O365 but I have been unsuccessful so far. I have tried everything on this microsoft document https://support.office.com/en-us/article/how-to-set-up-a-multifunction-device-or-application-to-send...

This is the Test notifications results.

I have replaced the email address for censoring purposes.

Last Test Result: (testemail@domain.com) Test e-mail failed; SMTP configuration error.
Last Server Response: 220 2.0.0 SMTP server ready
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:59 AM . Last Modified: ‎2024-03-11 12:18 AM

0 Likes
0
6753
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:59 AM . Last Modified: ‎2024-03-11 12:18 AM

Hi Kyle,

The firmware you gave me is from the UPS, not the NMC itself. I can tell from the screenshot of the NMC though the firmware on it is indeed a little older (since we've changed the UI in newer revs) so I recommend that you upgrade and retry. We made changes and updates to SSL/TLS email authentication that I think will benefit you here for Office 365. I think that is why it is failing. Let's try that next and see if any change post-upgrade.

You can get the latest firmware (6.5.6) for AP9630/31/35 in a Smart-UPS here (which I can tell it is a Smart-UPS based on the firmware you did provide)-> http://www.apc.com/shop/us/en/products/UPS-Network-Management-Card-v6-5-6-Firmware-for-Smart-UPS-Gal... (I suspect you are on 6.2.1 or earlier if you look under About->Network in the web UI.

(which, we have a new 6.6.4 coming in a matter of days, just  FYI.)

If you need any help applying the upgrade, please check here for available methods: http://www.apc.com/us/en/faqs/FA156047

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:59 AM . Last Modified: ‎2024-03-11 12:18 AM

0 Likes
0
6753
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:59 AM . Last Modified: ‎2024-03-11 12:18 AM

Hi Kyle,

I have a few questions/thoughts:

  • What firmware, especially AOS version is on your NMC2? We added TLS 1.2 for newer AOS versions which I think is required for this to work.
  • Did this ever work?
  • Can you share what settings you're using on the network management card side, specifically for Authentication mode - None, If Supported, Always, or Implicitly?
    • For my O365 setup, "Always" seems to work and be required.

For the rest, I am using smtp.office365.com, port 587. Then my email as the to/from address since I believe the "From Address" in the NMC needs to be a valid account as opposed to some dummy/made up address which I don't have control in our environment to create. For authentication, we have another username beyond the email within our domain to use, not sure if you have something similar.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:59 AM . Last Modified: ‎2024-03-11 12:18 AM

0 Likes
0
6754
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:59 AM . Last Modified: ‎2024-03-11 12:18 AM

This is a new UPS and is being setup for the first time. The firmware is the following: UPS 09.1(ID20)

Yes in the setup i had set TLS to always and on port 587. The account i was testing with is a legitimate mailbox and has a valid license for sending/receiving mail. I have the same from Address email that is under authentication.

tFjib4%2FVtJZmc9jFiezY1w%3D%3D.pngtFjib4%2FVtJZmc9jFiezY1w%3D%3D.png

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:59 AM . Last Modified: ‎2024-03-11 12:18 AM

0 Likes
0
6754
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:59 AM . Last Modified: ‎2024-03-11 12:18 AM

Hi Kyle,

The firmware you gave me is from the UPS, not the NMC itself. I can tell from the screenshot of the NMC though the firmware on it is indeed a little older (since we've changed the UI in newer revs) so I recommend that you upgrade and retry. We made changes and updates to SSL/TLS email authentication that I think will benefit you here for Office 365. I think that is why it is failing. Let's try that next and see if any change post-upgrade.

You can get the latest firmware (6.5.6) for AP9630/31/35 in a Smart-UPS here (which I can tell it is a Smart-UPS based on the firmware you did provide)-> http://www.apc.com/shop/us/en/products/UPS-Network-Management-Card-v6-5-6-Firmware-for-Smart-UPS-Gal... (I suspect you are on 6.2.1 or earlier if you look under About->Network in the web UI.

(which, we have a new 6.6.4 coming in a matter of days, just  FYI.)

If you need any help applying the upgrade, please check here for available methods: http://www.apc.com/us/en/faqs/FA156047

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore