Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 02:21 AM . Last Modified: 2024-02-29 10:11 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 02:22 AM . Last Modified: 2024-02-29 10:11 PM
Hi,
The reason for installing PowerChute on a system to to provide graceful shutdown. Why do you want to power down the VMs in the event of a power failure but not the host? If the host is not powered down it will crash.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 02:21 AM . Last Modified: 2024-02-29 10:11 PM
Hi,
Please review Schneider Electric FAQ FA159688
The ESXi host is responsible for powering down the VMs. The shutdown if the VMs is configured through Virtual Machine Startup/Shutdown on the host. Each of the VMs must have VMware tools installed on them for the host to be able to power them down.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 02:22 AM . Last Modified: 2024-02-29 10:11 PM
Hello,
yes i know that, the VMs are shutting down correctly. The problem is that the Host is also shutting down. But I don't want that.
ONLY the VMs should Shutdown.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 02:22 AM . Last Modified: 2024-02-29 10:11 PM
Hi,
The reason for installing PowerChute on a system to to provide graceful shutdown. Why do you want to power down the VMs in the event of a power failure but not the host? If the host is not powered down it will crash.