Newbie needs Help: PowerChute Network Shutdown for ESXi

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Newbie needs Help: PowerChute Network Shutdown for ESXi
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:11 PM

0 Likes
3
2514
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:11 PM

Newbie needs Help: PowerChute Network Shutdown for ESXi

Hi thanks in Advance,

we have a UPS lets say 90.90.90.2. A Host 90.90.90.30 and one ESXi-Host 90.90.90.31 on which are running two VMs (90.90.90.32, 33).

The ESXi VM Host again is just a Client running on a VM Vsphere Server on a different Network via VPN lets say 192.168.20.40.

I want to use PowerChute Network. I have installed it on the Host 90.90.90.30 as a Stand-Alone Host and entered the Configuration for the ESXi-Host 90.90.90.31. So far everything Ok.

But the Question is: How can I now shutdown the ESxi and the VMs ? There is no option available. No Menu where I can choose from. The only thing I can do is to program a batch file for using the shutdown settings. Is this the only option ? There is no Virtualization setting etc.

I think I have installed something wrong or installed the software on the wrong machine ?

What to do next ? These are all the Options I can choose: See picture.

Bildergebnis für powerchute network

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:11 PM

0 Likes
0
2513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:11 PM

Hi,

On 8/7/2017 11:01 AM, Dbdb said:

But when will the vms restart ?

Shut down and start up of the VMs is the responsibility of the ESXi host. See Schneider Electric FAQ FA159688

On 8/7/2017 11:01 AM, Dbdb said:

What is if the Computer on which PowerChute is installed is not working, will the VMs also shutdown ?

No. The host and the VMs will not be powered down. I recommend you install the PCNS Appliance on each host and configure that specific instance of PCNS to power down the corresponding host not a remote host.  

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:11 PM

0 Likes
0
2513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:11 PM

Hi,

In the PCNS web interface under Communications Settings enter the ip address, user name, and password for the host you would like PCNS to power down. Then under Configure Events select on battery or runtime remaining and enter a value that you would like PCNS to start the shutdown. See the help files for a description of both settings and you should read the PCNS VMware User's Guide. 

Example: UPS on battery event has been configured with a 120 second delay. The UPS switches to battery and PCNS is informed. PCNS wait 120 seconds to see if the event clears. It has not cleared so after the 120 delay PCNS begins the shutdown process. PCNS sends a signal the the configured ESXi host that it needs to power down. The host will then command the VMs down if the host has been configured to do so. See Schneider Electric FAQ FA159688 for assistance with configuring the ESXi host to power down the VMs. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:11 PM

0 Likes
0
2513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:11 PM

Thanks for your response.

My next question would be. Lets assume I have choose "battery exceeded" checked and entered 120 seconds. So when the battery is exceeded Power chute will advice VMware Host to shutdown. But when will the vms restart ? automatically ? Next question. What is if the Computer on which PowerChute is installed is not working, will the VMs also shutdown ?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:11 PM

0 Likes
0
2514
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:22 AM . Last Modified: ‎2024-02-29 10:11 PM

Hi,

On 8/7/2017 11:01 AM, Dbdb said:

But when will the vms restart ?

Shut down and start up of the VMs is the responsibility of the ESXi host. See Schneider Electric FAQ FA159688

On 8/7/2017 11:01 AM, Dbdb said:

What is if the Computer on which PowerChute is installed is not working, will the VMs also shutdown ?

No. The host and the VMs will not be powered down. I recommend you install the PCNS Appliance on each host and configure that specific instance of PCNS to power down the corresponding host not a remote host.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore