UPS NMC2 SMTP 554 respond code???

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS NMC2 SMTP 554 respond code???
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 11:24 PM . Last Modified: ‎2024-03-06 03:13 AM

0 Likes
3
1008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:24 PM . Last Modified: ‎2024-03-06 03:13 AM

UPS NMC2 SMTP 554 respond code???

Hi,

Recently i have installed an UPS with NMC2. SMTP has been configured and when i tried to send a test email, I received an error "SMTP configuration error".

Using wireshark to capture traffic between UPS and SMTP server, i notice that after smtp command "RCTP TO: emailaddress" is sent to SMTP server, SMTP server replies with a respond code 554: Relay rejected for policy reason.

Anyone encountered it before? Do you have any suggest solution?

Thanks.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:24 PM . Last Modified: ‎2024-03-06 03:13 AM

0 Likes
0
1008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:24 PM . Last Modified: ‎2024-03-06 03:13 AM

ok, is this stuff actually accurate?

EmailServerName=SMTPserver@mydomain
EmailFromName=UPSname@mydomain
EmailReceiver1Address=user1@mydomain
EmailReceiver2Address=user2@mydomain
EmailReceiver3Address=user3@mydomain
EmailReceiver4Address=user4@mydomain

it seems very generic. i assume it us based on what you said but you might want to double check it. you will also wanted take a look at the bottom of this knowledgebase: http://nam-en.apc.com/app/answers/detail/a_id/7957

it refers to NMC2 and different firmwares.

lastly, we recently released a new firmware for Smart UPS or Symmetra single phase firmware - AOS 5.1.5 and sumx or sy 5.1.5. you may want to check out.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:24 PM . Last Modified: ‎2024-03-06 03:13 AM

0 Likes
0
1008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:24 PM . Last Modified: ‎2024-03-06 03:13 AM

that sounds like an email server problem. you probably want to find out from your email administrator to make sure you are using the correct information within the NMC for your network. it sounds like it may not be correct and your SMTP server does not support/allow SMTP relay, based on the error message you are seeing.

if you want, please post your config.ini file following [these instructions|http://nam-en.apc.com/app/answers/detail/a_id/9321]. i really need only the NetworkEmail section of it if you'd like to delete everything else.

thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 11:24 PM . Last Modified: ‎2024-03-06 03:13 AM

0 Likes
0
1007
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:24 PM . Last Modified: ‎2024-03-06 03:13 AM

Thanks for your reply.

The UPS i mentioned was installed at one of branch office. Firmware version is 5.1.3. All UPS at HQ site with older firmware version is able to send email with the same list of recipients. So i'm not sure if it is SMTP server configuration or not.

Following is NetworkEMAIL from config.ini:

[NetworkEMAIL]
; To change an E-mail Recipient's Password use the
; EmailReceiver#Password keyword where # is the number of the
; recipient. i.e., EmailReceiver1Password=password
EmailServerName=SMTPserver@mydomain
EmailFromName=UPSname@mydomain
EmailReceiver1Address=user1@mydomain
EmailReceiver2Address=user2@mydomain
EmailReceiver3Address=user3@mydomain
EmailReceiver4Address=user4@mydomain
EmailReceiver1Route=Local
EmailReceiver2Route=Local
EmailReceiver3Route=Local
EmailReceiver4Route=Local
EmailReceiver1Enable=enabled
EmailReceiver2Enable=enabled
EmailReceiver3Enable=enabled
EmailReceiver4Enable=enabled
EmailReceiver1Format=Long
EmailReceiver2Format=Long
EmailReceiver3Format=Long
EmailReceiver4Format=Long
EmailReceiver1Language=enUs
EmailReceiver2Language=enUs
EmailReceiver3Language=enUs
EmailReceiver4Language=enUs
EmailReceiver1Username=User
EmailReceiver2Username=User
EmailReceiver3Username=User
EmailReceiver4Username=user

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:24 PM . Last Modified: ‎2024-03-06 03:13 AM

0 Likes
0
1009
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:24 PM . Last Modified: ‎2024-03-06 03:13 AM

ok, is this stuff actually accurate?

EmailServerName=SMTPserver@mydomain
EmailFromName=UPSname@mydomain
EmailReceiver1Address=user1@mydomain
EmailReceiver2Address=user2@mydomain
EmailReceiver3Address=user3@mydomain
EmailReceiver4Address=user4@mydomain

it seems very generic. i assume it us based on what you said but you might want to double check it. you will also wanted take a look at the bottom of this knowledgebase: http://nam-en.apc.com/app/answers/detail/a_id/7957

it refers to NMC2 and different firmwares.

lastly, we recently released a new firmware for Smart UPS or Symmetra single phase firmware - AOS 5.1.5 and sumx or sy 5.1.5. you may want to check out.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore