Dear all
our client installed this Galaxy VS, Galaxy PX UPS and they need the % of load output power per phase.
Someone has any idea?
Modbus Register Map attached
thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-05 03:25 AM
Hello,
There is a modbus register that provide 16 bit integer value for the The percentage of the UPS system capacity presently used across all phases. only The load percentage for the highest phase load is displayed as per the attachment