UPS Galaxy VS, Galaxy PX % load power used Modbus register
Dear all
our client installed this Galaxy VS, Galaxy PX UPS and they need the % of load output power per phase.
Someone has any idea?
Modbus Register Map attached
thanks in advance
- Tags:
- english
Authentication Failed.
- Authentication Ticket Mismatched, failed authentication.
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-05 03:25 AM
Hello,
There is a modbus register that provide 16 bit integer value for the The percentage of the UPS system capacity presently used across all phases. only The load percentage for the highest phase load is displayed as per the attachment
Regards,
Karim
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-05 03:25 AM
Hello,
There is a modbus register that provide 16 bit integer value for the The percentage of the UPS system capacity presently used across all phases. only The load percentage for the highest phase load is displayed as per the attachment
Regards,
Karim