Symmetra PX with 2 of external battery bank, can have a different count of batt in each bank ?
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-09-3009:13 PM
Symmetra PX with 2 of external battery bank, can have a different count of batt in each bank ?
Dear all, we have 1 symmetra px with 2 external power bank which is split into 48 pcs batt each ( total 96 pcs batt ) right now in bank 1 there is 2 batt is broken make all the bank 1 is not working with bank 2 still working correctly, is it possible that we take out 2 the dead batt, resulting in, 46 pcs batt in bank 1 and 48 pcs batt in bank 2 or should be setup to 47 pcs batt for each bank
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-0503:18 AM
Hello,
It seems you had Symmetra PX 250/500 unit,it is recommended to keep the number of blocks is 48 per string ( maximum three strings or 144 cells ) as it is recommended to keep 288 VDC in both positive and negative wi side of the batteries (or 576 VDC nominal) to get the most optimized runtime ,but no issues if only maximum 2 cells for each string is not available
The UPS supports customer-specific battery solutions with 144 cells (+/- 6 cells) for runtime optimization. The display has settings for number of cells on DC voltage levels (V/cell)
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-0503:18 AM
Hello,
It seems you had Symmetra PX 250/500 unit,it is recommended to keep the number of blocks is 48 per string ( maximum three strings or 144 cells ) as it is recommended to keep 288 VDC in both positive and negative wi side of the batteries (or 576 VDC nominal) to get the most optimized runtime ,but no issues if only maximum 2 cells for each string is not available
The UPS supports customer-specific battery solutions with 144 cells (+/- 6 cells) for runtime optimization. The display has settings for number of cells on DC voltage levels (V/cell)
Regards,
Karim