Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

UPS: Compensating for high input voltage

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS: Compensating for high input voltage
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
cduncan
cduncan
Cadet

Posted: ‎2024-07-24 06:47 AM

0 Likes
1
979
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-24 06:47 AM

UPS: Compensating for high input voltage

Hi folks,

 

Recently our UPS is sending us notices that it's compensating for high input voltages.  With a Code: 0x010D.   I haven't found any threshold settings for input voltages, I see under Power Settings that there is an Output Upper Limit and Lower Limit, is this the threshold that this alert runs against?

 

It's set to 127.  I can see in the data log that Vmax is hitting 126 pretty consistently at different periods of times for hours and the notifications seem to match logs.

If all that adds up can you please tell me if 127 is the correct setting and what it impact to our equipment if the UPS is output hot.  When Vmax is at 126 Vout is 126 also.  Can this hurt equipment.   Can you also tell me what might cause out input/output to be so high?

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Teken
Kirk Teken
Kirk

Posted: ‎2024-07-24 07:43 AM . Last Modified: ‎2024-07-24 07:51 AM

0 Likes
0
973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-24 07:43 AM . Last Modified: ‎2024-07-24 07:51 AM

Depending upon which specific model APC UPS. There will be 1-3 power management options available for you to adjust to meet your environmental needs.

 

Sensitivity: Generally speaking this setting determines the acceptable input power quality to be used. The labels can be seen as normal, low, high, etc.

 

The sensitivity determines when the unit will go into battery only mode. As such if the unit constantly goes into battery only mode it will always provide the cleanest inverted output voltage (power) to the connected outputs. 

The downside is the obvious reduction in battery service life. ☝️ The batteries are rated for 2-5 years of service based on (Usage, Temperature, and Environmental Factors).

 

The sensitivity also monitors the frequency and THD. As such this normally detects what people often call *Dirty Power* as this also monitors very brief changes in input voltage: Sag, Surge, Spike, etc.

 

Transfer Voltage: Adjusting the upper and lower transfer voltage determines when the unit will engage and remain in AVR mode.

 

The unit simply engages the different transformer taps to Boost / Trim the voltage to the output thus providing an acceptable voltage to the connected loads.

 

Generally speaking there is no harm to the electronics when the AVR is engaged. But you should be aware you’ll see a increase / decrease in the power consumption. Devices that are so called PFC (Power Factor Correcting) do not always behave well when the input voltage swings high / low.

 

Bypass: This forces the unit to receive power directly from the AC Mains. This bypasses the battery circuit / inverter depending upon model. 

 

NOTE: Every APC Enterprise UPS has a (Relay Weld) error code. This directly relates to the system transferring over from online vs battery only power and to a lesser extent when the AVR circuit is enabled.

 

Meaning repeated transfers will reduce the service life of the UPS. As each time the relay changes state it induces (contact arc) which pits, melts, the internal contacts.

 

Let me know if this answers your question. If so please consider marking this as a solution to help the next person asking the same. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore