Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

UPS: Bypass not in range ; distorted waveform and SNMP shutdown signal

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS: Bypass not in range ; distorted waveform and SNMP shutdown signal
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
LaXaRuS
LaXaRuS
Cadet

Posted: ‎2021-09-30 11:29 AM . Last Modified: ‎2021-09-30 11:35 AM

0 Likes
1
2506
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-30 11:29 AM . Last Modified: ‎2021-09-30 11:35 AM

UPS: Bypass not in range ; distorted waveform and SNMP shutdown signal

Hello,

I did have some problem with the shutdown signal from NMC3 and servers.

My servers are getting power from SRT5KXLI with built in NMC3. They are configured to wait until low battery before safe shutdown.

A couple of days ago, UPS detected "UPS: Bypass not in range ; distorted waveform" and UPS started feeding the devices from the battery due to this.

However, my servers went immediately to the safe shutdown without waiting for "low battery". Later on when I tried to reproduce the issue by cutting the input power of the UPS, servers were still on as should be since UPS battery was full.

I would like to ask when UPS detects distorted waveform, does it send shutdown signal through SNMP?

Furthermore, how can I simulate a distorted waveform so that I can debug this issue?

Some details:

Green mode is disabled and UPS is on online mode.

Network firmware: v1.5.1.1

Model number: 0N-1557

Hardware Revision: 3

Thanks in advance

Attachments
Labels
  • Labels:
  • Datacenter UPS
  • Smart-UPS & Symmetra LX-RM
  • UPS Management Devices & PowerChute Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
LlewellynITPS
LlewellynITPS
Cadet

Posted: ‎2022-01-18 05:46 PM

0 Likes
0
2332
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-18 05:46 PM

Hi Laxarus,

 

Do you have a the loading for the UPS as well as the expected runtime?

You should look at the event to to see when the event occurred and then go to the data log to see what the readings were around the time of the event. The default data log interval is normally 10min and we reduce that down to 1 min or 60 sec (the lowest interval). Normally the only time the unit goes onto battery during such an event is if set thresholds were exceeded.

 

You should see if the data log shows what the battery charge % dropped to since the shutdown command will only be sent if the % reaches the 4 min +1 min mark in your case.

 

You would not be able to reproduce the distorted wave form without specific switching equipment for the UPS input under controlled conditions. If you had a large HVAC system you can try turning that on/off to see if the system can reproduce the distortion. Would only look at these options if this was a constant issue.

 

The main points you can look at is the amount of load on site and the runtime predicted by your system. In our experience there is very little you can do about distortion on the input.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore