Posted: β2021-07-01 06:21 AM . Last Modified: β2024-03-04 11:46 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:21 AM . Last Modified: β2024-03-04 11:46 PM
Updated two SMX750's in two different physical locations this morning to 6.2 firmware. After the update, both UPS's are throwing this error:
Critical - UPS: An internal UPS communication fault exists.
Error code is Code : 0x0172. Haven't tried to downgrade yet, but I haven't seen anyone else online or in these forums with a similar problem. Has anyone else had issues upgrading to 6.2? Once location has NMC2 with environmental and the other location has no environment, both with the same error.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:23 AM . Last Modified: β2024-03-04 11:44 PM
Hi Gregory, yes, I still see the updates. I informed the case owner how it should've been handled. Sorry about that.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:21 AM . Last Modified: β2024-03-04 11:46 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:21 AM . Last Modified: β2024-03-04 11:46 PM
Scratch that, can't downgrade.
10/24/14: 22:56:30 172.16.0.8: Testing device connection
10/24/14: 22:56:30 172.16.0.8: Device connection passed
10/24/14: 22:56:31 172.16.0.8: Testing FTP Log-in
10/24/14: 22:56:34 172.16.0.8: FTP Log-in passed
10/24/14: 22:56:35 172.16.0.8: Saving data file
10/24/14: 22:56:38 172.16.0.8: ERROR --> Disallow AOS downgrade
10/24/14: 22:56:38 172.16.0.8: AOS Downgrade not allowed: 620-->606
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:21 AM . Last Modified: β2024-03-04 11:46 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:21 AM . Last Modified: β2024-03-04 11:46 PM
I am having this problem as well after upgrading firmware to 6.20 on AP9630 NMCs on a number of different Smart-UPS models including the SMX750. Seems all software these days is suspect. The problem occurs at certain times of the day only, not 24 hours a day. Very strange.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:21 AM . Last Modified: β2024-03-04 11:45 PM
Let me see if I can investigate what this event is triggered by and if it has changed recently.
In the meantime, if anyone is interested in downgrading, you can use a manual method like FTP (explained here ->How do I upgrade the firmware on an APC Network Management Card (NMC) or NMC embedded device (Rack P...) . The older wizard/upgrade utility versions blocked downgrading but I had them adjust that for future versions of the wizard/upgrade utility, especially for users who purchase a standalone Network Mgmt Card and it comes with Smart-UPS firmware and need to put it in a different device - it was treating that as a "downgrade." So, post v6.2.0, if you want to downgrade back to v6.2.0, the wizard/upgrade utility will let you.
Also, I noticed both of you are saying you're seeing this on SMX750. Can you tell me the firmware versions on the UPS? It will be under About->UPS in the v6 firmware web UI of the Network Management Card. I need something like UPS 03.8 (ID12) or whatever it says.
Thanks!
Edit/Update: Based on what I learned, I essentially need to see some additional files from the UPS/Network Management Card to look at this further. Ideally, please provide the "single file download/dump" available via About->Support or logzip CLI command because it will have the file I need (Instructions here-> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...) No major changes were made to this event and when it appears in v6.2.0 so the problem may be with the particular UPS and it reporting a particular flag or something.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:22 AM . Last Modified: β2024-03-04 11:45 PM
Thank you!
The UPS firmware is a bit older. My first thought is that we should try upgrading it which I believe the latest version for ID11 is UPS 03.8. I have a feeling the UPS firmware is the issue here. The only downfall to getting these log files is that the fault appears to be "cleared" right now when you extracted the files for me so there is a file that can tell us information about the fault when it is currently active. I am using an SMX1500 ID11 at my desk coincidently with v6.2.0 and have never seen this alarm. I highly doubt all your UPSs have an internal fault either based on what you've described.
Anyway, I think the best thing to do on at least this one UPS is upgrade it to UPS 03.8 and see if it still throws the alarm periodically. If it does, then I'll need this dump of files when the Internal Communication Fault is active.
Details on upgrading the firmware are here - the only caveat is that the UPS output must be turned off -> How do I update the firmware of my SMT, SMX, SMC, or SRT series Smart-UPS? | FAQs | Schneider Electr... explains how to do it via a serial cable (or USB if supported) and then How do I upgrade my SMT/SMX/SRT Smart-UPS firmware using my AP9630/AP9631 Network Management Card? |... explains how to do it via your AP9630 and have it push the right file to your UPS - I believe this UPS should support upgrading via the NMC (as opposed to the Firmware Upgrade Wizard via serial cable) but the UPS I have of that type is already at UPS 03.8 but the UPS appears to support upgrading via NMC (since you already have one). You need to put SMX11UPS_03-8.enc file on any ID11 device, or least this one to start and test to see what happens.
This event I think is only supported by SMX/SMT/SRT type UPSs so you wouldn't see it on older SU, SUA, or SUM type.
Let me know if you have any questions before proceeding.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:22 AM . Last Modified: β2024-03-04 11:45 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:22 AM . Last Modified: β2024-03-04 11:45 PM
Thanks - I will try that. This will take me a little time since I cannot shut the UPS outputs off most of the time. But I'll report back once I am able to do this.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:22 AM . Last Modified: β2024-03-04 11:45 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:22 AM . Last Modified: β2024-03-04 11:45 PM
Angela - you assisted me in getting a replacement NMC in this thread (Cannot Upgrade AP9631 with SUMX/AOS 5.0.3 and BootMon 1.0.0) - got the replacement card, upgraded to SUMX/AOS 6.2.0 & Bootmon 1.0.8 successfully and now I'm experiencing the same errors in the logs as well. I'm also at UPS 02.2 (ID11). It's interesting to note that the logs show this error only occurs between 7pm and Midnight - see log below
In attempting to use the NMC to update the UPS firmware following the link you posted ( Frequently Asked Questions ), I was able to FTP the correct enc file to the upsfw directory, but when I get to step 3, there is no Firmware update page in the web UI in 6.2.0 as described here:
Check the firmware update page with the NMC web UI to see that the update file is loaded onto the card.
β’ For v5.1.X firmware, this page is under UPS tab->Configuration->Firmware Update
β’ For v6.X.X firmware, this page is located under Configuration->Firmware Update
Not sure how to proceed with updating the UPS firmware - see screenshot below showing Firmware Update option not listed.
.
Network Management Card AOS v6.2.0
Smart-UPS & Matrix-UPS APP v6.2.0
Date Time Name Contact Location System IP
12/10/2014 03:02:46 apc88DB05 Unknown Unknown 192.168.1.61
Date Time User Event Code
12/10/2014 00:00:16 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/09/2014 23:01:21 Device UPS: An internal UPS communication fault exists. 0x0172
12/09/2014 23:00:16 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/09/2014 22:01:21 Device UPS: An internal UPS communication fault exists. 0x0172
12/09/2014 22:00:16 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/09/2014 21:01:21 Device UPS: An internal UPS communication fault exists. 0x0172
12/09/2014 21:00:16 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/09/2014 20:01:21 Device UPS: An internal UPS communication fault exists. 0x0172
12/09/2014 20:00:16 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/09/2014 19:01:20 Device UPS: An internal UPS communication fault exists. 0x0172
12/09/2014 00:00:17 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/08/2014 23:01:22 Device UPS: An internal UPS communication fault exists. 0x0172
12/08/2014 23:00:17 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/08/2014 22:01:21 Device UPS: An internal UPS communication fault exists. 0x0172
12/08/2014 22:00:17 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/08/2014 21:01:21 Device UPS: An internal UPS communication fault exists. 0x0172
12/08/2014 21:00:16 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/08/2014 20:01:21 Device UPS: An internal UPS communication fault exists. 0x0172
12/08/2014 20:00:16 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/08/2014 19:01:21 Device UPS: An internal UPS communication fault exists. 0x0172
12/08/2014 00:00:08 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/07/2014 23:01:22 Device UPS: An internal UPS communication fault exists. 0x0172
12/07/2014 23:00:07 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/07/2014 22:01:22 Device UPS: An internal UPS communication fault exists. 0x0172
12/07/2014 22:00:07 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/07/2014 21:01:22 Device UPS: An internal UPS communication fault exists. 0x0172
12/07/2014 21:00:07 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/07/2014 20:01:22 Device UPS: An internal UPS communication fault exists. 0x0172
12/07/2014 20:00:07 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/07/2014 19:01:21 Device UPS: An internal UPS communication fault exists. 0x0172
12/07/2014 00:00:15 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/06/2014 23:01:20 Device UPS: An internal UPS communication fault exists. 0x0172
12/06/2014 23:00:15 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/06/2014 22:01:20 Device UPS: An internal UPS communication fault exists. 0x0172
12/06/2014 22:00:15 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/06/2014 21:01:20 Device UPS: An internal UPS communication fault exists. 0x0172
12/06/2014 21:00:15 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/06/2014 20:01:20 Device UPS: An internal UPS communication fault exists. 0x0172
12/06/2014 20:00:15 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/06/2014 19:01:20 Device UPS: An internal UPS communication fault exists. 0x0172
12/06/2014 00:00:08 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/05/2014 23:01:24 Device UPS: An internal UPS communication fault exists. 0x0172
12/05/2014 23:00:09 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/05/2014 22:01:15 Device UPS: An internal UPS communication fault exists. 0x0172
12/05/2014 22:00:10 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/05/2014 21:01:17 Device UPS: An internal UPS communication fault exists. 0x0172
12/05/2014 21:00:12 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/05/2014 20:01:17 Device UPS: An internal UPS communication fault exists. 0x0172
12/05/2014 20:00:12 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/05/2014 19:01:18 Device UPS: An internal UPS communication fault exists. 0x0172
12/05/2014 00:00:14 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/04/2014 23:01:19 Device UPS: An internal UPS communication fault exists. 0x0172
12/04/2014 23:00:14 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/04/2014 22:01:20 Device UPS: An internal UPS communication fault exists. 0x0172
12/04/2014 22:00:15 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/04/2014 21:01:21 Device UPS: An internal UPS communication fault exists. 0x0172
12/04/2014 21:00:16 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/04/2014 20:01:20 Device UPS: An internal UPS communication fault exists. 0x0172
12/04/2014 20:00:15 Device UPS: An internal UPS communication fault no longer exists. 0x0173
12/04/2014 19:01:20 Device UPS: An internal UPS communication fault exists. 0x0172
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:22 AM . Last Modified: β2024-03-04 11:45 PM
Hi apoulias - can you give me the first six characters of your UPS serial number? Something like AS0937? I also am interested in the CBL version but I have an ID11 at my desk with 6.2.0 and I cannot see it via the NMC. Can you make sure the LCD menu on the UPS is in Advanced mode and check the About menu there and confirm you see the CBL version as 1.something?
With ID11 and UPS 02.2, I have a feeling you'll need to run through a special procedure to update the bootloader (CBL) on this UPS to get it to UPS 03.8. I just want to confirm and if that is the case, then I will send you those instructions to get the UPS upgraded as I believe the bootloader is older so it does not support upgrading the UPS via the NMC.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:22 AM . Last Modified: β2024-03-04 11:45 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:22 AM . Last Modified: β2024-03-04 11:45 PM
SMX1500RM2UNC
First 6 of the UPS SN =AS101513
From the LCD
UPS Firmware 1 UPS 02.2
UPS Firmware 2 COM 02.3
UPS Firmware 3 UBL 05.0
UPS Firmware 4 CBL 01.0
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:22 AM . Last Modified: β2024-03-04 11:45 PM
Ok, I suspected correctly. I'll send you a private message with a special procedure you'll need to do. Please read carefully and let me know if you have any questions before you get started but to get this particular UPS updated, you'll need to upgrade the CBL with a special script (via serial connection), get it to firmware UPS 03.7, and then you can use the NMC (if you want) or continue via serial to get to the latest rev for ID11 UPS, UPS 03.8.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:22 AM . Last Modified: β2024-03-04 11:45 PM
I also have this same problem on a bunch of id11's I just upgraded the nmc's on to 6.2 to fix a radius problem and am now getting the connection problems messages. I have the same firmware levels, could you send me the special procedure needed to upgrade the firmware to 3.8?
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:22 AM . Last Modified: β2024-03-04 11:45 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:22 AM . Last Modified: β2024-03-04 11:45 PM
I am also having the same issue with a ID11 UPS. I have the same firmware levels. Could you please send me the special procedure needed to upgrade the firmware to 3.8?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:22 AM . Last Modified: β2024-03-04 11:45 PM
Hi,
Tech support is up to speed on this issue. I created a knowledge base article -> http://www.apc.com/support/index?page=content&country=ITBβ©=en&locale=en_US&id=FA241461
At this time, Peter anyone else with this issue, please contact technical support via phone or email (http://www.apc.com/site/support/index.cfm/contact-information/) and just reference this knowledge base article and let them know you require the procedure mentioned in the article and they can easily send it to you and provide guidance. We have just streamlined how we can provide support for this issue as it is difficult for me to be the only one sending out instructions to everyone.
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:22 AM . Last Modified: β2024-03-04 11:45 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:22 AM . Last Modified: β2024-03-04 11:45 PM
Angela - Can you please send me this special procedure. I have been unable to get it from APC support. They keep sending me the normal NMC / Wizard procedure which does not work for this case. They tell me there is no other procedure.
Thanks - Paul
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:22 AM . Last Modified: β2024-03-04 11:45 PM
Hi Paul, do you have a case or reference number I can get someone to look at for the disconnect in providing the procedure, please? I am trying to avoid being the only one that can figure out how to send this procedure, especially when my presence here on the forum is dwindling due to a new role. I also want to inform whoever it is what the process is.
I'll send you the procedure via a private message here but it is important to me that I follow up with tech support.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:22 AM . Last Modified: β2024-03-04 11:45 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:22 AM . Last Modified: β2024-03-04 11:45 PM
Angela - I've tried a few times recently. Here is the most recent case - #2788-499424333-5645
Thanks - Paul
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:22 AM . Last Modified: β2024-03-04 11:45 PM
I have the same issue, can i get the procedure?
thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:22 AM . Last Modified: β2024-03-04 11:45 PM
On 10/26/2015 1:11 PM, Angela said:I'll send you the procedure via a private message here but it is important to me that I follow up with tech support.
I am having the same issue. I have contacted support, and they know nothing about a special upgrade procedure. I did share your knowledgebase reference with the support agent. I can send you the case number for reference if needed. Please PM the special procedure.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:22 AM . Last Modified: β2024-03-04 11:45 PM
They sent this:
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:22 AM . Last Modified: β2024-03-04 11:45 PM
ohh. and there seems to be a bug that if you run the Runtime Calibration, it seems to work, but it will always display that it is still Running even after its done. Seems the only way to clear that is to reset the UPS. and its a PIA to power off all my devices to do so. π
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:23 AM . Last Modified: β2024-03-04 11:45 PM
Thank you very much Jason! I will go through the procedure in detail before proceeding. It seems that I am getting about a half-dozen "UPS: An internal UPS communication fault exists" errors between the hours of 7pm and midnight every day. For now, I have just turned off the alert notification of that error. I will have to wait until I can power down my loads before attempting the upgrade. I'm wondering if there are any issues with the "UPS: An internal UPS communication fault exists" error, other than cluttering up the log.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:23 AM . Last Modified: β2024-03-04 11:44 PM
Prior to the update the runtime calibration would always fail with an error about the load level (which was constant), and it showed i had only a 30-45min runtime. I have the internal battery as well as the external battery chassis (with two new battery strings). My load level was only 15-20%. Right now, at 17.5% load it shows runtime of 3hr and 50min π
I personally think it was causing an issue, and i always seemed to get the alerts at night as well. strange. Its been up 63 days now since updating and the only thing in the logs are normal items, NTP sync, occasional High voltage compensation from Mains..but no UPS fault logs at all.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:23 AM . Last Modified: β2024-03-04 11:44 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:23 AM . Last Modified: β2024-03-04 11:44 PM
I too have the error, and firmware...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:23 AM . Last Modified: β2024-03-04 11:44 PM
A few posts up i attached the files along with the docs APC sent with the step by step procedure.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:23 AM . Last Modified: β2024-03-04 11:44 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:23 AM . Last Modified: β2024-03-04 11:44 PM
LOL...I see that now.
The link was very small, and I totally missed it.
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:23 AM . Last Modified: β2024-03-04 11:44 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:23 AM . Last Modified: β2024-03-04 11:44 PM
Jason -
Any idea if I can use the Network card to upgrade the firmware?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:23 AM . Last Modified: β2024-03-04 11:44 PM
You need to use the serial interface for the initial upgrade steps. The text file shows the steps. I did some googling and found the serial pin out online. Was able to make my own cable as I did not have the factory cable.
After itβs up to date with the firmwares I attached I think further updates may be supported for Network mgmt card.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:23 AM . Last Modified: β2024-03-04 11:44 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:23 AM . Last Modified: β2024-03-04 11:44 PM
Thanks Jason!
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:23 AM . Last Modified: β2024-03-04 11:44 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:23 AM . Last Modified: β2024-03-04 11:44 PM
Hey Angela -
I'm not sure if you are still monitoring this thread, but it seems like support techs still don't know about your FAQ.
I referenced it in the request I opened, and they just told me it's too old, and can't be updated.
48910935
Thank you for finding a way to do it.
π
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 06:23 AM . Last Modified: β2024-03-04 11:44 PM
Hi Gregory, yes, I still see the updates. I informed the case owner how it should've been handled. Sorry about that.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2023-05-07 05:21 PM
Please send me the procedure as well. I need to update mine from 2.2 to 3.7/3.8. Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2023-05-18 10:52 AM
I'm having this same issue with eleven SMX1500RM2U units and one SU1400RMXLB3U unit. A of them have an AP9631 card running the latest version firmare. Downgrading is not an option for me either.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2024-08-12 01:43 PM
i have the same error see related post of my self SMX3000HV ap9631 - Schneider Electric Community (se.com)
can you support me with this error?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2025-10-27 01:00 PM
So after an extended power outage my SMX1000I (ID:11) died and after the power comeback the behavior is like this:
- NMC gives 0x0172
- Doesn't display any details about itself, eg. model and serial number is 12121212...
So tried following after removing the NMC:
- Brain dead reset
- FW upgrade from above instructions, nothing happens
- FW upgrade with the latest wizard and tried SMX11UPS_03-7.enc, SMX11UPS_03-8.enc... the UPS refuses it due to a list of reasons like battery disconnect, no ac power, etc, however none are actual
Further more the lates FWU sees the current FW as (literal) squares and when I press more info, only COM 03.8 and CBL 02.1 are shown.
Other observations:
- each time it starts it asks to enter the basic setup, eg. set the language, date, etc.
- each time I set the menu to advanced it jumps right back to standard.
So any ideas on how to resurrect it before I do surgery on it ?
/Alex
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2025-11-13 10:27 PM
Alex I have this exact same problem. Did you find any resolution?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2025-11-14 09:39 AM
Unfortunately not, I was hoping that someone here might bring some light.
Also due to time constrains, surgery needs to wait probably until Christmas when I will have some free time.
My wild guess is that some mem chip gave up after the power outage, making it forget everything about itself.
How did you ended up in the same situation ?
Link copied. Please paste this link to share this article on your social media post.