UPS: An extended run frame fault exists.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS: An extended run frame fault exists.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 05:46 AM . Last Modified: ‎2024-03-19 12:34 AM

0 Likes
2
5561
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:46 AM . Last Modified: ‎2024-03-19 12:34 AM

UPS: An extended run frame fault exists.

I have one of the Symmetra PX 80KVA with two additional battery frame. Since a week this shows message as "Extended Run Frame fault". The error message cleares itself in 20 secs "Extended Run Frame fault cleared". This happens few times a day. The battery frame communicaton is good and reports the right number of batteries and reports battery quantity increased and decreased messages. Is there are real problem with the extended frame or these are junk messages?

Thanx

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:46 AM . Last Modified: ‎2024-03-19 12:34 AM

0 Likes
0
5555
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:46 AM . Last Modified: ‎2024-03-19 12:34 AM

Hi,

You said:
"The first bit of good news: an Extended Run Frame Fault does not impact the operation of your UPS. "

An Apc technical guy told me the same and few month after a string of batteries burn inside this frame....

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:46 AM . Last Modified: ‎2024-03-19 12:34 AM

0 Likes
0
5555
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:46 AM . Last Modified: ‎2024-03-19 12:34 AM

Hello,

The first bit of good news: an Extended Run Frame Fault does not impact the operation of your UPS. Even in those moments when the frame fault is present, it is possible the UPS may not see the batteries, so the UPS runtime estimate would be off. However, since the batteries are still physically connected, they would still provide backup to the system in the event of a power outage.

The pieces involved in the XR frame fault would be:
• the XR com card in the UPS and XR frame,
• The cable that runs between the XR com cards,
• the terminators in the XR com cards,
• the battery monitor cards in the XR frame,
• the power supply in the XR frame.
• Correct frame address on the XR frame

Since your issue is intermittent, it will be a little hard to track down.

The easiest things to start with are:
• try a new RJ-45 cable between the cabinets (perhaps there is a loose connection somewhere)
•check the terminators in the XR com cards
-->Typically if you have a UPS and 1 XR frame, there will be a terminator and a RJ-45 cable in each XR com card. (if you have multiple XR frames, you will have a terminator in the UPS, and the last XR frame).
• try your setup with the two terminators as described above, and then try it with both terminators removed (I found it surprising, but I have occasionally observed removing the terminators to resolve faults)

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:46 AM . Last Modified: ‎2024-03-19 12:34 AM

0 Likes
0
5556
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:46 AM . Last Modified: ‎2024-03-19 12:34 AM

Hi,

You said:
"The first bit of good news: an Extended Run Frame Fault does not impact the operation of your UPS. "

An Apc technical guy told me the same and few month after a string of batteries burn inside this frame....

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of