SYMMETRA PX 160KW backup time issue

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SYMMETRA PX 160KW backup time issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 05:46 AM . Last Modified: ‎2024-03-19 12:34 AM

0 Likes
1
606
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:46 AM . Last Modified: ‎2024-03-19 12:34 AM

SYMMETRA PX 160KW backup time issue

Dear Team,
We are facing Backup time issue with Symmetra PX 160K. 48 PLP battery module install in UPS and XR frame UPS showing backup time 7hr 1 minute on NMC. The detail is given below.

UPS load 7.8 % (please see attached ( run time screen shot)
Battery Capacity 100% charged.(please see attached ( run time screen shot)
No of battery Module 48 PLP ( Please see attached # of battery screen shot)
Showing Run time 7hr1 minute on NMC .(please see attached ( run time screen shot) but we test UPS backup time physically UPS provided backup time 3 hr 9 minute (please see attached backup time results screen shot.)
UPS
Model SY32K160H-PD (with two additional Power Modules SYPM10k16H)
Serial # PD1117160068
XR Frame Qty 1

Message was edited by: zakir

Attachments
FFC ISD.7z
Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:46 AM . Last Modified: ‎2024-03-19 12:34 AM

0 Likes
0
606
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:46 AM . Last Modified: ‎2024-03-19 12:34 AM

hello, someone from our 3 phase support team was gracious enough to review your question. here is what I got back:

Unfortunately I am unable to view the screenshots.

There are two main things to consider when runtime is involved, the estimated time and actual time.

The estimate time is based on 4 things:
-The number of batteries
-The battery charge
-The Load on the UPS
-The battery calibration factor

Actual runtime is based on all those factors, plus the actual age and health of the batteries.
- since your batteries are coming up on two years old, you actual runtime will be less then the predicted runtime.


There are some reasons why the estimated rutime may be too high.
-The first is that your load is so low. There is certainly no issue with having a lightly loaded UPS, but runtime estimations increase exponentially as load approaches 0. So very small loads may have high reported runtimes.
-We also mentioned that batteries have less runtime as they age. If you have never done a run-time calibration on the UPS, you could run one, and see if the UPS adjusts its runtime estimation
-there is also one setting that should be checked. In your network interface, go to UPS-> Configuration -> General, and ensure that the "external battery cabinet" is set to 0 Amp-Hour

A sanity check you can perform. Run a UPS self test, note the values for battery voltage, runtime, and battery capacity before and after the test - also note how long the test runs for. Generally the runtime remaining after a self test would be much closer to your actual runtime.

For further details, you can always open a support ticket with the technical center for your region:
www.apc.com (select your country/region)-> Support -> contact us

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:46 AM . Last Modified: ‎2024-03-19 12:34 AM

0 Likes
0
607
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:46 AM . Last Modified: ‎2024-03-19 12:34 AM

hello, someone from our 3 phase support team was gracious enough to review your question. here is what I got back:

Unfortunately I am unable to view the screenshots.

There are two main things to consider when runtime is involved, the estimated time and actual time.

The estimate time is based on 4 things:
-The number of batteries
-The battery charge
-The Load on the UPS
-The battery calibration factor

Actual runtime is based on all those factors, plus the actual age and health of the batteries.
- since your batteries are coming up on two years old, you actual runtime will be less then the predicted runtime.


There are some reasons why the estimated rutime may be too high.
-The first is that your load is so low. There is certainly no issue with having a lightly loaded UPS, but runtime estimations increase exponentially as load approaches 0. So very small loads may have high reported runtimes.
-We also mentioned that batteries have less runtime as they age. If you have never done a run-time calibration on the UPS, you could run one, and see if the UPS adjusts its runtime estimation
-there is also one setting that should be checked. In your network interface, go to UPS-> Configuration -> General, and ensure that the "external battery cabinet" is set to 0 Amp-Hour

A sanity check you can perform. Run a UPS self test, note the values for battery voltage, runtime, and battery capacity before and after the test - also note how long the test runs for. Generally the runtime remaining after a self test would be much closer to your actual runtime.

For further details, you can always open a support ticket with the technical center for your region:
www.apc.com (select your country/region)-> Support -> contact us

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of