Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Getting battery runtime correct for a Symmetra LX with a SYAOPT4 cable
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
The manual shows it connecting to an "external Non APC" battery array"
To me this means I can connect a giant 120vdc battery array with some good HRL12500W batteries to my Symmetra 16k LX.
It seems like a great solution to avoid the low quality, short lifetime and overly expensive SYBT5 architecture.
My question, is without the battery communication cable and battery cabinet brain...
How will the Symmetra LX know it has the additional battery cabinet.
How will it figure runtime?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2605:46 AM. Last Modified: 2024-03-1912:34 AM
there is an option via the installed network management card (and maybe the powerview..?) to add amp hours for external battery cabinets so that the UPS can factor in that "dumb" external cabinet and help provide a more accurate runtime estimate. i don't think that the UPS could every technically report more than 24 hours 0 minutes which may not even be realistic anyway.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2605:46 AM. Last Modified: 2024-03-1912:34 AM
there is an option via the installed network management card (and maybe the powerview..?) to add amp hours for external battery cabinets so that the UPS can factor in that "dumb" external cabinet and help provide a more accurate runtime estimate. i don't think that the UPS could every technically report more than 24 hours 0 minutes which may not even be realistic anyway.