Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

APC Smart-UPS VT 15KVA 3Phase - SUVT15KH2B2S - Queries about bypass voltage

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC Smart-UPS VT 15KVA 3Phase - SUVT15KH2B2S - Queries about bypass voltage
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Anonymous user
Not applicable

Posted: ‎2021-06-26 05:46 AM . Last Modified: ‎2024-03-19 12:34 AM

0 Likes
0
494
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:46 AM . Last Modified: ‎2024-03-19 12:34 AM

APC Smart-UPS VT 15KVA 3Phase - SUVT15KH2B2S - Queries about bypass voltage

Hi,

We have a SUVT15KH2B2S, and at one of our sites we've been experiencing power fluctuations, brownouts. We've seen an input voltage drop down to 208volts from the normal ~230v. We have our servers and SAN equipment connected to this UPS which is obviously very sensitive to any power fluctuations. The UPS is clearly working as it should as the output voltage all the time is 230v even when the voltage is dropping.

Anyway, i'm seeing this message: "An input voltage or frequency problem prevents switching to bypass mode." when we see the voltage drop down to 208 volts, obviously i won't switch to bypass mode, and risk the damage to the equipment connected.

The reason I ask the following questions is, i've been told by my manager to ensure that if the voltage drops so low the batteries replace it and then the servers begin to shutdown (as we only have about 30 minutes on batteries) that I must switch to bypass mode to ensure the servers keep running. To put it in his words "I don't want the UPS we bought to protect us, deciding when to close our business!."

Obviously I think this is irresponsible to do this, so I won't, I'm just trying to collect some evidence to back up my cause.

I've identifed the cause of our voltage drop being the supply distribution board being very overloaded (i'm working on getting budget to get it upgraded), rated at 315A per phase, its drawing up to 335A per phase when the voltage begins to drop! Plus some of the insulation on the wires is melting and dripping on the floor. 😞 Oh and if that wasn't bad enough the distribution board and power switchgear was installed in 1956! 😞

So

My questions are:
*1. When does it kick the battery in, just how low does the voltage need to go before the battery starts replacing the input mains supply? I need to know how far we are off the battery having to supliment the supply because of this?*

*2. At voltages around 208 volts what kind of damage could happen to our servers and SAN equipment connected? I've always used the rule of thumb: "constant power = fewer IT problems!"*

Thanks for any advice or thoughts you might have.

g

Message was edited by: geekmungus

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now