UPS APC SUA1500I cannot Cold Start
I have UPS APC SUA1500I, replaced new battery but I cannot cold start. When plugged in UPS run normal But when I Unplugged In UPS sound Beep and Power Off. And Cannot Cold start Although Plugg in UPS run normal.
Pls hep,
- Labels:
-
Smart-UPS & Symmetra LX | RM
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:33 AM . Last Modified: 2024-03-18 12:22 AM
Glad you fixed it.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-28 07:33 AM . Last Modified: 2024-03-18 12:22 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:33 AM . Last Modified: 2024-03-18 12:22 AM
Nobody can help me.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:33 AM . Last Modified: 2024-03-18 12:22 AM
Hi,
Have you checked the voltage reading of the battery to see if it is good?
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:33 AM . Last Modified: 2024-03-18 12:22 AM
I don't think you connected the battery completely. Check the connections and then plug in the unit for a few hours while it is off to charge the battery. Then test to see how it is working.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-28 07:33 AM . Last Modified: 2024-03-18 12:22 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:33 AM . Last Modified: 2024-03-18 12:22 AM
I have replaced Capacity 250V - 2.2uF. Now, It run OK!
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:33 AM . Last Modified: 2024-03-18 12:22 AM
Glad you fixed it.