UPS 8000RT Fault and battery LEDs are lit

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS 8000RT Fault and battery LEDs are lit
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 11:35 PM . Last Modified: β€Ž2024-03-11 04:45 AM

0 Likes
5
1485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 11:35 PM . Last Modified: β€Ž2024-03-11 04:45 AM

UPS 8000RT Fault and battery LEDs are lit

Hello.

I have an APC UPS 8000RT, when I turn it on, after half a second, it cuts the power from its loads and lights up (as shown on attached picture):
Fault LED and Battery LEDS number 3 and 5 (counting from the top in upright tower orientation)

Could anyone hint me on what the problem could be?

Is there a document or a site that could help decode LED error messages?


!http://www.apc-forums.com/servlet/JiveServlet/download/25-11514-43704-2871/faulty-apc-ups-front-pane...!


more information on the UPS that could help diagnosing:

That UPS is only turned on occasionally for a few hours, being shut down and disconnected from mains most of the time.
It is connected to mains around once a week, and has enough time to fully charge its baterries.
It still shows same error with no loads or other cables attached, except for power mains.
It has never run on batteries, except for the normal power-on tests.
It has mostly servers as its loads, consuming nearly 70% of its max power.
It does not have external batteries attached.
It did not show signs of any problem until now.
Other UPS of exact same model powers the same servers normally.

Message was edited by: sultansaraev

Message was edited by: sultansaraev

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 11:35 PM . Last Modified: β€Ž2024-03-11 04:44 AM

0 Likes
0
1485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 11:35 PM . Last Modified: β€Ž2024-03-11 04:44 AM

hello.

this is generally diagnosed by tech support so how to read the LEDs is not public.

i looked up your combination and it appears to be a problem with the output relay. my first initial thought is that because you turn it on and off so often, that could be related to the output relay failure but i have no evidence to back that up. most of the time, UPSs are just left on and don't turn off. i just say that because I imagine if the UPS is turning on and off often that possibly the output relay is moving often but i am not even sure if that is how this UPS is designed.

have you logged into the network management card (that is pre-installed) and verified if there is any other evidence to what lead up to this? there also may be additional information on the failure.

i would check that first and then depending what it says, we could try to reset/braindead the UPS but it is likely this is a hard fault and may need to be replaced.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 11:35 PM . Last Modified: β€Ž2024-03-11 04:44 AM

0 Likes
0
1486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 11:35 PM . Last Modified: β€Ž2024-03-11 04:44 AM

hello.

this is generally diagnosed by tech support so how to read the LEDs is not public.

i looked up your combination and it appears to be a problem with the output relay. my first initial thought is that because you turn it on and off so often, that could be related to the output relay failure but i have no evidence to back that up. most of the time, UPSs are just left on and don't turn off. i just say that because I imagine if the UPS is turning on and off often that possibly the output relay is moving often but i am not even sure if that is how this UPS is designed.

have you logged into the network management card (that is pre-installed) and verified if there is any other evidence to what lead up to this? there also may be additional information on the failure.

i would check that first and then depending what it says, we could try to reset/braindead the UPS but it is likely this is a hard fault and may need to be replaced.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 11:35 PM . Last Modified: β€Ž2024-03-11 04:44 AM

0 Likes
0
1485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 11:35 PM . Last Modified: β€Ž2024-03-11 04:44 AM

Thank you very much for your reply!


It indeed looks like some sort of output relay problem. (The load IS powered for a split-second however, but I don't know what's inside that UPS either)

I have not realized that a network management card could be still functioning even if though the UPS failed and does not power anything; I will check that ASAP.

Unfortunately, it is not possible to keep that UPS constantly on, since the power mains is turned off at night. We have many RT-type UPS working that way for years, and this one was the first that failed, after less than a year of somewhat-infrequent use.

I will do as you said and probably ship the UPS to the nearest repair facilty, now that I know it is not likely a battery/mains/software fault.

Message was edited by: sultansaraev

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 11:35 PM . Last Modified: β€Ž2024-03-11 04:44 AM

0 Likes
0
1485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 11:35 PM . Last Modified: β€Ž2024-03-11 04:44 AM

yes, as long as the UPS electronics are energized, regardless of power output, the management card should be accessible.

here are some helpful articles to help get you started with the management card (located in the knowledge base - http://www.apc.com/site/support/index.cfm/faq/)

β€’ FA156064
β€’ FA156131

let me know if you need anything else.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 11:35 PM . Last Modified: β€Ž2024-03-11 04:44 AM

0 Likes
0
1484
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 11:35 PM . Last Modified: β€Ž2024-03-11 04:44 AM

Thank you again for your replies, they were very helpful. I need no further information (at least for now).

Despite all efforts, I could not get any response from both the COM-port and network management card (I connected same cords to a neighbor UPS of same model, and that one worked; the network card was probably never configured, but it does not react to any configuration utilities or DHCP servers; rechecked everything and cold rebooted everything many times).

But it is clear to me that the problem is not in the cabling, batteries, power mains, firmware, or misconfiguration - that is, I cannot fix the problem myself. So the UPS is awaiting repairs now.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 11:35 PM . Last Modified: β€Ž2024-03-11 04:44 AM

0 Likes
0
1484
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 11:35 PM . Last Modified: β€Ž2024-03-11 04:44 AM

what model management card is it? does it have lights on it at least?

if its an older style card, it defaults to DHCP/BOOTP but the DHCP address will not be accepted unless DHCP option 43 is configured on your server.

also what serial cable did you use? you need to use an APC specific serial cable and certain port settings.

if you decide you want to revisit the management card, let me know as that is my expertise as a matter of fact πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore