UPS 3000 XLM strange behaviour

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS 3000 XLM strange behaviour
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:56 AM . Last Modified: ‎2024-03-12 04:53 AM

0 Likes
3
1164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:56 AM . Last Modified: ‎2024-03-12 04:53 AM

UPS 3000 XLM strange behaviour

Hello,

APC SMART UPS 3 KVA 1phase in / 1 phase out with add. 48V battery pack. (APC-SUM3000RMXLI2U +  2 * APC-SUM48RMXLBP2U) . Purchased and installed  in 2013 on remote unmanned site. External power is very unstable.  After some time we noticed the following situation (taken from SNMP messages  log) :

Sep 12 15:26:50 UPS: On battery power in response to an input power problem. 0x0109

Sep 12 15:26:52 UPS: No longer on battery power. 0x010A

Sep 12 15:27:52 UPS: In bypass in response to an internal hardware fault. 0x011B

Sep 12 15:27:53 UPS: The internal battery temperature exceeds the critical threshold. 0x012C

Sep 12 15:27:54 UPS: Refused a self-test; UPS is overloaded. 0x0106

at the same time diagnostic showed

  Internal temperature: 27° C,

  Enviroment temperature: 24° C

  UPS Load: 12%, 1,7A

  Input voltage: 228V

  Input frequency: 50Hz

After switching to bypass diagnostic had been showing continuous discharge of batteries. In one hour  UPS turned off and site was   deenergized.      When we arrived on site and manualy swithed UPS on it returned to normal operation but in several days the situation repeated. Question : is it 100% hardware problem or could be some solutions?

Thanks in advance and look forward for any help!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:56 AM . Last Modified: ‎2024-03-12 04:53 AM

0 Likes
0
1164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:56 AM . Last Modified: ‎2024-03-12 04:53 AM

Can you tell me any specific things you want me to look at in the event log which corresponds to what you did and what happened to the UPS on its own? I see a lot of on battery events earlier in the log.

I see the battery voltage on the unit very low and it seemed to be because the UPS was in bypass at some point around 8/21 but we don't have a data log that far back. I also see runtime calibrations started - this should only be done when you have a problem with the reported runtime - is someone issuing runtime calibrations?

A couple of comments:

  • When you restart the management card, it has nothing to do with restarting the UPS. You'd need to do that under the UPS control section of the management card to reboot the output. To do a full restart on the UPS and restart it completely, you'll need to braindead it. To braindead, you turn the attached load off and turn the UPS off. Remove any cables attached (which if using a management card, there should be no USB or serial cable attached). Then unplug the UPS from AC power and hold down the off (o) button on the front of the UPS until the UPS clicks and/or flashes its LEDs to discharge completely. Then you can reconnect it to AC power, turn it back on, and plug your attached load back in.
  • I need to better understand what events in the log are caused by you or your team versus which that you believe the UPS was logging on its own.
  • I think its possible that the battery temperature (versus the UPS internal temperature) is getting too hot and maybe the UPS is putting itself in bypass to prevent further charging and damage to the battery. It could be that the battery is just faulty from the factory and could require a warranty replacement.
  • Someone or something (10.32.3.4 and 10.32.1.19) keeps trying to do runtime calibrations and this is concerning. Why are we doing that??

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:56 AM . Last Modified: ‎2024-03-12 04:53 AM

0 Likes
0
1164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:56 AM . Last Modified: ‎2024-03-12 04:53 AM

It sounds like you have a battery problem. Are the UPS internal batteries and external battery pack batteries all the same age? If so, it sounds like they are failing. If they are different ages (which isn't good since they should all be replaced at the same time), then we'd need to narrow down the culprit. A failing battery can damage good batteries on the same bus though.

The "refused a self test; UPS is overloaded" message can also indicate failing batteries that overload the inverter when on battery.

Can you provide the full event.txt, data.txt and config.ini files? Instructions are here -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...

Anyway, I'd probably also visually inspect all batteries and beware they may be warm to the touch if they are damaged and/failing. There is also an event in the log about a high internal temperature. If you find problems, it might be best to disconnect all batteries from the system to prevent them from charging further and causing more problems.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:56 AM . Last Modified: ‎2024-03-12 04:53 AM

0 Likes
0
1163
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:56 AM . Last Modified: ‎2024-03-12 04:53 AM

Hello,

Thanks for quick answer! But I don't think that its the battery problem. All batteries and the UPS are new. Installation and setup was made about two month ago.

We tryed to restart UPS (both through WEB interface and through SNMP) - no any effect, it simply refused to restart. We restarted management card - it's rebooted, but no any affect again. In some time the UPS turned output power off and we've lost connection because a network equipment is powered from that UPS frown.

When our staff arrived on site, the UPS was in turned off state. The UPS was turned on by power button and showed that it worked on batteries, at the same time, through WEB interface, it showed that the UPS charged the battery, which is strange. After that, power button was pressed again and UPS went on main power.

Our staff checked all batteries and they seemed are OK - no any damages and its voltage is OK too. So they cleaned all electrical contacts and checked all mounting and connection, reassembled all UPS parts, fully charged batteries and producedrecalibration. Setup the sensitivity to Low. Now we are watching this UPS. In the near future we are planing to install automatic voltage regulator with hope that it help to make work of equipment more stable.

I've attached log files and config.ini, may be they will be helpful. As I can see - after the UPS had turned off the output power - it worked and collected information about input power, but it didn't turned  the output power on because it thought that it had some fault. The only fault it had (by log)  - "The internal battery temperature exceeds the critical threshold", but on UPS diagnostic - internal temperature never does not exceed 28 degress of C. So it is intresting - how does the UPS determine battery temperature?

Sorry for long post, hope that it gives some clues for finding solution to our problem.

Attachments
data.txt.zip
event.txt.zip
config.ini.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:56 AM . Last Modified: ‎2024-03-12 04:53 AM

0 Likes
0
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:56 AM . Last Modified: ‎2024-03-12 04:53 AM

Can you tell me any specific things you want me to look at in the event log which corresponds to what you did and what happened to the UPS on its own? I see a lot of on battery events earlier in the log.

I see the battery voltage on the unit very low and it seemed to be because the UPS was in bypass at some point around 8/21 but we don't have a data log that far back. I also see runtime calibrations started - this should only be done when you have a problem with the reported runtime - is someone issuing runtime calibrations?

A couple of comments:

  • When you restart the management card, it has nothing to do with restarting the UPS. You'd need to do that under the UPS control section of the management card to reboot the output. To do a full restart on the UPS and restart it completely, you'll need to braindead it. To braindead, you turn the attached load off and turn the UPS off. Remove any cables attached (which if using a management card, there should be no USB or serial cable attached). Then unplug the UPS from AC power and hold down the off (o) button on the front of the UPS until the UPS clicks and/or flashes its LEDs to discharge completely. Then you can reconnect it to AC power, turn it back on, and plug your attached load back in.
  • I need to better understand what events in the log are caused by you or your team versus which that you believe the UPS was logging on its own.
  • I think its possible that the battery temperature (versus the UPS internal temperature) is getting too hot and maybe the UPS is putting itself in bypass to prevent further charging and damage to the battery. It could be that the battery is just faulty from the factory and could require a warranty replacement.
  • Someone or something (10.32.3.4 and 10.32.1.19) keeps trying to do runtime calibrations and this is concerning. Why are we doing that??

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of